Written against the 2026 NEC and checked section by section, September 2026
Voltage Drop Practice Questions
For an ordinary branch circuit or feeder the code sets no percentage, because the 3 and 5 percent figures everybody quotes sit in informational notes and the code says its own notes are not requirements. Two articles make a limit enforceable, and the paper tests the arithmetic in both cases. These 25 items run the formula forward and backward, in single phase and three phase, off Chapter 9 Table 8, and sort out where a real limit lives.
Pick an answer and the explanation opens with the section it comes from. These are original questions written for this site, not questions from the exam. Have your own code book open: the Texas exam is open book, and looking the section up is the skill being tested.
Read the voltage drop study page first if the topic is new to you.
1. What does the code require for voltage drop on an ordinary branch circuit?
Show the answer
A. No percentage at all, since the figures are in an informational note
The branch-circuit note describes a conductor sized so the drop at the farthest outlet stays inside 3 percent, with the total across feeder and branch circuit inside 5, and calls that reasonable efficiency of operation. That is a description of good practice rather than a rule. An item asking what the code requires has an answer, and any percentage sitting in the options is there to be left alone.
NEC 2026 210.19
2. How does the code classify its own informational notes?
Show the answer
B. As explanatory material that is not enforceable as a requirement
The code sorts its text into mandatory rules, permissive rules and explanatory material, and puts informational notes in the third bucket by name. Mandatory rules are marked by shall and shall not, permissive ones by shall be permitted and shall not be required. Once you have that sorting, the whole voltage drop question answers itself without any arithmetic.
NEC 2026 90.5(A), 90.5(B), 90.5(C)
3. Where does the matching voltage drop note for feeders sit?
Show the answer
C. At 215.4(A)(2)
The feeder minimum rating and size section carries the note under its ampacity adjustment and correction subdivision, and the branch-circuit note points across at it by number. Both notes carry the same figures for the same reason. Knowing where the pair lives is worth more than the numbers, because an item usually asks which text is enforceable rather than what the percentage is.
NEC 2026 215.4(A)(2)
4. What two figures do the branch-circuit and feeder notes name?
Show the answer
D. 3 percent at the farthest outlet and 5 percent total across feeder and branch circuit
The 3 belongs to the branch circuit at its farthest outlet and the 5 is the total once the feeder is added in, and both notes state it the same way. The third option has the two numbers the right way round but assigned backwards, which is how an item collects somebody who remembers a pair of figures without remembering which is which.
NEC 2026 210.19, 215.4(A)(2)
5. Why does the single phase voltage drop formula carry a multiplier of 2?
Show the answer
A. Because the current travels out on one conductor and back on the other
The conductor the current actually sees is the round trip, so a load 150 feet away sits at the end of 300 feet of copper. Nothing about it is a safety factor, which matters because a safety factor would be something you could argue about and this is not. Picture the path before you write anything and the multiplier stops being something you memorize.
NEC 2026 210.19
6. What multiplier replaces the 2 on a three phase circuit?
Show the answer
B. 1.732
The square root of three takes the place of the 2 because the three phase currents sit 120 degrees apart and their drops do not simply add. The 0.866 option is that same square root divided by two, which is the ratio between the two answers rather than the multiplier itself, so it produces a number that looks reasonable and is wrong by a factor of two.
NEC 2026 210.19
7. Which length goes into the formula?
Show the answer
C. The one way length in both versions
Use the one way distance in both, because the multiplier already carries the return path. Doubling the length and then multiplying by 2 as well doubles the answer, and using the one way length with no multiplier at all halves it. Those two errors and the wrong multiplier are one mistake wearing different clothes, and all three come from not picturing the path first.
NEC 2026 210.19, 215.4(A)(2)
8. Where does the direct current resistance used in a voltage drop calculation come from?
Show the answer
D. Chapter 9 Table 8
Table 8 gives direct current resistance in ohms per 1000 feet, and it splits copper from aluminum, solid from stranded, and coated copper from uncoated. Chapter 9 Table 1 is raceway fill percentages and answers a different question entirely. Divide the per thousand figure by 1000 to get ohms per foot, or keep it in thousands and divide the length instead. Mixing the two is a factor of a thousand and you will notice.
NEC 2026 Chapter 9 Table 8
9. A 120 volt single phase circuit carries 15 amperes 120 feet to a load on 12 AWG stranded uncoated copper, listed at 1.98 ohms per 1000 feet. What is the voltage drop?
Show the answer
A. 7.13 volts
Two times 120 feet times 15 amperes is 3600, and 3600 times 0.00198 ohms per foot is 7.13 volts. Halving it to 3.56 is the one way length with no multiplier. The 6.95 answer uses the solid copper figure of 1.93 instead of the stranded one, which is the right arithmetic off the wrong row of the table.
NEC 2026 Chapter 9 Table 8
10. What is that drop as a percentage of the supply voltage?
Show the answer
B. 5.94 percent
Divide 7.13 by 120 and you get 5.94 percent, which is well past the figure the notes describe. Nothing in the code stops that circuit being installed, and nothing at the end of it will thank you either. The 3 and 5 percent options are the figures from the notes rather than the answer to the arithmetic, which is a distinction items on this subject lean on hard.
NEC 2026 210.19
Ten down. If you want these timed and scored by content area, the practice exam runs thirty questions free, and the full bank of 178 plus the calculation ladder is $79 once.
11. A 480 volt three phase circuit carries 40 amperes 250 feet on 6 AWG copper, listed at 0.491 ohms per 1000 feet. What is the voltage drop?
Show the answer
C. 8.50 volts
Multiply 1.732 by 250 feet by 40 amperes to get 17,320, then by 0.000491 ohms per foot for 8.50 volts. Using the single phase multiplier of 2 gives 9.82, which is close enough to look right and is the answer of somebody who read the current and skipped the phases. Doubling the length as well gives 17.0.
NEC 2026 Chapter 9 Table 8
12. What is that three phase drop as a percentage?
Show the answer
D. 1.77 percent
Divide 8.50 by 480 and you get 1.77 percent, comfortably inside what the note describes. Higher voltage is what buys that: the same volts lost are a smaller share of a bigger number, which is the whole reason long runs get designed at 480 rather than 208. Divide by the system voltage, not by the drop, and not by the voltage at the load.
NEC 2026 215.4(A)(2)
13. A 240 volt single phase circuit carries 40 amperes 150 feet on 6 AWG aluminum, listed at 0.808 ohms per 1000 feet. What is the voltage drop?
Show the answer
A. 9.70 volts
Two times 150 times 40 is 12,000, and 12,000 times 0.000808 is 9.70 volts. The 5.89 answer is the same run worked on the copper row at 0.491, which is the mistake of reading the size correctly and the material wrongly. Aluminum of the same size has roughly two thirds the conductivity, so it drops proportionally more over the same distance.
NEC 2026 Chapter 9 Table 8
14. Chapter 9 Table 8 separates its copper resistance figures how?
Show the answer
B. By solid and stranded construction, and by coated and uncoated copper
Four copper figures can apply to one size and picking the wrong one is a quiet error, because the answer stays in a plausible range. The table also prints circular mil area and overall diameter, and a note gives the equation for correcting resistance to a temperature other than 75 degrees. Insulation type does not appear, because the resistance belongs to the metal and not the jacket.
NEC 2026 Chapter 9 Table 8
15. When would you use Chapter 9 Table 9 instead of Table 8?
Show the answer
C. When the item introduces power factor or reactance rather than treating the circuit as purely resistive
Table 9 gives alternating current resistance and reactance for conductors in a raceway, with columns for the raceway material and effective impedance figures at a stated power factor. Table 8 is direct current resistance and treats the run as a plain resistor. A stem that hands you a power factor is telling you which table it wants, and answering it out of Table 8 throws away the input it gave you.
NEC 2026 Chapter 9 Table 8, Table 9
16. A run is upsized to hold voltage drop down. What else changes?
Show the answer
D. Nothing but the wire
A 20 ampere circuit run in 10 AWG for distance is still a 20 ampere circuit, protected at 20 amperes and limited to what a 20 ampere circuit may supply. One thing does follow the wire: where ungrounded conductors are increased in size, the wire type equipment grounding conductor is increased proportionally, which is a rule in Article 250 rather than a voltage drop rule.
NEC 2026 210.19, 250.122
17. A 208 volt three phase circuit carries 50 amperes 200 feet and you want to hold the drop to 3 percent. What is the smallest uncoated stranded copper conductor?
Show the answer
A. 4 AWG
Three percent of 208 is 6.24 volts. Divide that by 1.732 times 200 feet times 50 amperes, which is 17,320, to get 0.00036 ohms per foot, or 0.36 ohms per 1000 feet. In the uncoated copper column 6 AWG is 0.491 and misses, and 4 AWG is 0.308 and clears it. Going to 2 AWG works too but is larger than the calculation asks for.
NEC 2026 Chapter 9 Table 8
18. A 240 volt single phase circuit carries 60 amperes 175 feet and you want to hold the drop to 3 percent. What is the smallest aluminum conductor?
Show the answer
B. 2 AWG
Three percent of 240 is 7.2 volts. Divide by 2 times 175 feet times 60 amperes, which is 21,000, to get 0.000343 ohms per foot, or 0.343 per 1000 feet. In the aluminum column 4 AWG is 0.508 and misses while 2 AWG is 0.319 and clears. Running the same numbers on the copper column lands you two sizes small, which is why the material has to be read out of the stem first.
NEC 2026 Chapter 9 Table 8
19. Working the calculation backward, which way do you round when the answer falls between two sizes?
Show the answer
C. Toward less resistance, which means toward the larger conductor
You solved for a maximum resistance, so any conductor at or below that figure works and anything above it fails the target you set. A conductor one size small is the option an item will put in the list on purpose, because it looks like the natural rounding and it misses. Ampacity is a separate check that the answer still has to pass on its own.
NEC 2026 Chapter 9 Table 8
20. Which article makes a voltage drop percentage an enforceable requirement for sensitive electronic equipment?
Show the answer
D. Article 647, at 1.5 percent on a branch circuit and 2.5 percent combined
The tight numbers are the reason that article exists, and they sit in enforceable text rather than in a note. The article covers a separately derived system at 120 volts line to line and 60 volts to ground, used in commercial or industrial occupancies under close supervision by qualified personnel. A candidate carrying the slogan that voltage drop is only a recommendation gets this one wrong.
NEC 2026 647.1, 647.5(D)
21. Within that same article, what limit applies to a branch circuit supplying receptacles?
Show the answer
A. 1 percent, with the load taken as 50 percent of the branch-circuit rating and a combined limit of 2.0 percent
The cord-connected case is tighter than the fixed equipment case, and it tells you what load to calculate with, which is unusual. The stated purpose is to hold the drop to 1.5 percent once a portable cord is added on the end of the branch circuit, so the extra half percent is the cord. Fixed equipment on Chapter 3 wiring methods stays at 1.5 and 2.5.
NEC 2026 647.5(D)
22. For a fire pump, what limit applies at the contactor load terminals with the motor running?
Show the answer
B. Not more than 5 percent below the motor voltage rating with the motor at 115 percent of its full load current rating
Notice the shape of it. The measurement is taken at 115 percent of full load rather than at full load, so the calculation you run is not the one the stem first appears to ask for. It is also referenced to the motor voltage rating and not to the controller rated voltage, which is the reference the starting limit uses. Two limits, two reference points, two conditions.
NEC 2026 695.7, 695.8
23. What relieves a fire pump installation of the motor starting voltage drop limit?
Show the answer
C. Mechanical starting on emergency run, or bypass operation of a variable speed pressure limiting controller, where the start is shown to work on the standby system
Two named conditions, and each one carries the same proof: somebody has to show the machine starting on the standby supply rather than assume it will. That demonstration is what the exception is buying, so an option that names the equipment and drops the demonstration has taken half the sentence. The running limit at the load terminals is a separate subsection and neither exception reaches it.
NEC 2026 695.8
24. A single phase circuit drops 12 volts. The same current, the same distance and the same conductor on a three phase circuit drops what?
Show the answer
D. 10.4 volts
Only the multiplier changed, so the new answer is the old one times 1.732 divided by 2, which is 12 times 0.866, or 10.4 volts. That gives you a check worth carrying: if your three phase answer comes out larger than your single phase answer on identical inputs, you have swapped the multipliers. The 13.9 option is the same arithmetic done upside down.
NEC 2026 215.4(A)(2)
25. A conductor satisfies every ampacity rule in the book and still delivers unusable voltage at the far end. What does the code say about that?
Show the answer
A. The ampacity rules do not take voltage drop into consideration, and the notes at 210.19 and 215.4(A)(2) address it separately
The ampacity section says so in its own informational note and points at both voltage drop notes by number. That is why the two calculations are run separately and why the larger of the two answers is what you install. Derating is about the conductor heating up and voltage drop is about the load starving, and neither calculation can see the other one.
NEC 2026 310.14(A)
One question a day keeps the habit, the practice exam runs the clock, and the tools page has the calculators and games.