Written against the 2026 NEC and checked section by section, September 2026
Boxes and Conduit Bodies Practice Questions
One box on one drawing generates three separate items, and they are answered from three separate places: whether an enclosure is needed, whether this one is big enough, and whether it is supported, deep enough and reachable once it is in. These questions work 300.17 and 300.16 for where enclosures go, 314.16(C) and 314.28 for the two sizing methods that are not box fill, and 314.23 through 314.29 for support, depth, weight and access. The 2026 addresses are used throughout.
Pick an answer and the explanation opens with the section it comes from. These are original questions written for this site, not questions from the exam. Have your own code book open: the Texas exam is open book, and looking the section up is the skill being tested.
Read the boxes and conduit bodies study page first if the topic is new to you.
1. How does Article 100 define a conduit body?
Show the answer
C. A separate portion of a conduit or tubing system giving access through a removable cover at a junction of two or more sections or at a terminal point
The definition ties the enclosure to the raceway system it is part of, at a junction or at a terminal point, with access through a removable cover. The same definition adds that FS and FD boxes, and larger cast or sheet metal boxes, are not classified as conduit bodies. That last sentence decides items where a stem calls an FD box a conduit body to see whether you will follow along.
NEC 2026 Article 100
2. In the 2026 edition, which section says where a box, conduit body or fitting is required?
Show the answer
D. 300.17
The general requirement sits at 300.17 in the 2026 book, having been 300.15 in the edition before it. Its neighbor moved too: the free conductor rule that used to be 300.14 is now 300.16. In an open book exam the navigation is the part that costs minutes, so the safe habit is to find requirements by part title and heading rather than by an address you memorized from an older book.
NEC 2026 300.17
3. A fitting identified for the use stands in for a box or conduit body under what conditions?
Show the answer
A. No conductor is spliced or terminated inside it, and where it serves as a pull point it stays accessible after installation
Two conditions travel together in that subdivision: nothing spliced and nothing landed inside, and if it is doing the job of a pull point, you can still get at it once the building is finished. An item on this topic usually describes an installation with no box in it and asks whether that is acceptable, which means the answer lives in an exception rather than in the general sentence. Size and location listing are conditions from other rules entirely.
NEC 2026 300.17(F)
4. Cable with a nonmetallic sheath enters a box through a cable clamp. How far does the sheath extend inside the box?
Show the answer
B. 1/4 inch
The sheath extends not less than a quarter inch inside the box, and the same quarter inch beyond the end of any cable clamp. The reason is abrasion: the point where the conductors leave the sheath is the vulnerable spot, and it belongs inside the enclosure. That quarter inch shows up in several places in this article, so check which one a stem is asking about before you answer.
NEC 2026 314.17(B)(2)
5. Nonmetallic sheathed cable enters a single gang nonmetallic box no larger than a nominal 2-1/4 by 4 inches, mounted in a wall. When is securing the cable to the box not required?
Show the answer
D. Where the cable is fastened within 8 inches of the box measured along the sheath and the sheath extends through the knockout at least a quarter inch
The exception carries a box size, a fastening distance measured along the sheath, and a sheath extension, and all three have to be true together. The distance is 8 inches measured along the sheath rather than the 12 inches people carry from the cable article. Multiple cable entries through one knockout are permitted under the same exception, which is the part that makes it practical.
NEC 2026 314.17(B)(2)
6. A conduit body encloses 6 AWG and smaller conductors with nothing spliced, tapped or mounted inside. How is it sized?
Show the answer
C. Its cross sectional area is at least twice that of the largest conduit or tubing it can be attached to, and the conductor count comes from the conduit fill table
Used purely as a pull point, a conduit body is sized against the raceway rather than against the conductors, and both comparisons come out of conduit fill rather than out of volume. There is no cubic inch total anywhere in that branch and no conductor count in the box fill sense. That is a clean decision rather than a judgment call, and it turns on whether anything is spliced, tapped or mounted inside.
NEC 2026 314.16(C)(1)
7. What has to be true before a conduit body may contain a splice, a tap or a wiring device?
Show the answer
B. The manufacturer has durably and legibly marked it with its volume
The marking is the gate. Only a conduit body marked by its manufacturer with its volume is permitted to contain a splice, a tap or a wiring device, and once it does, the conductor count comes from the box fill calculation. The raceway area comparison does not disappear when the splice arrives; box fill is added to it rather than substituted for it.
NEC 2026 314.16(C)(2)
8. A splice is made up inside a service entrance elbow that encloses 6 AWG conductors. What is the code position?
Show the answer
A. Short radius bodies of that kind are not permitted to contain splices, taps or wiring devices at all
Capped elbows and service entrance elbows exist only to let you install the raceway and pull the conductors through, and the subsection says they do not get a splice, a tap or a wiring device whatever they are marked with. A stem describing a splice in one of them is describing a violation rather than a sizing problem. The volume marking is a distractor in that scenario, not the answer.
NEC 2026 314.16(C)(3)
9. What decides whether an enclosure is sized by the fill calculation or by the pull and junction box method?
Show the answer
D. Whether the conductors it encloses reach 4 AWG
Conductor size is the first fork and it is sharp, because there is no trade size between 6 AWG and 4 AWG for anything to fall into. Boxes and conduit bodies enclosing 4 AWG or larger comply with the pull and junction box section, which sizes from geometry rather than from volume. Whether a device is mounted matters, but only on the 6 AWG and smaller branch and only for conduit bodies.
NEC 2026 314.16, 314.28
10. An angle pull is made in a junction box. The largest raceway in that row is 2 inch trade size and it is the only entry in the row. What is the minimum distance from that entry to the opposite wall?
Show the answer
B. 12 inches
An angle pull, a U pull or a splice measures six times the trade size of the largest raceway in the row, so six times 2 inches gives 12 inches. The eight times multiplier belongs to a straight pull and produces the 16 inches offered here. Sketching the enclosure with its raceways first is what tells you which case you are in, because the case follows from the picture rather than from the wording.
NEC 2026 314.28(A)(2)
Ten down. If you want these timed and scored by content area, the practice exam runs thirty questions free, and the full bank of 178 plus the calculation ladder is $79 once.
11. A row on one wall of a junction box has three raceway entries for an angle pull, at 3 inch, 2 inch and 2 inch trade sizes. What minimum distance from that row to the opposite wall does the section require?
Show the answer
C. 22 inches
Start with six times the largest raceway in the row, which is 18 inches, then increase it by the sum of the diameters of all the other entries in that same row on that same wall, which is 2 plus 2, or 4 inches. That gives 22 inches. Each row is figured on its own and the row producing the greatest distance is the one used, so a box with entries on several walls needs the calculation run more than once.
NEC 2026 314.28(A)(2)
12. Two raceway entries enclose the same conductor. How far apart do they have to be?
Show the answer
A. Not less than six times the trade size of the larger raceway
The section gives both the enclosure dimension and the distance between entries carrying the same conductor, and the second one is six times the trade size of the larger raceway. Items are written to hand you both numbers and see which one you report, so read whether the question wants the box dimension or the spacing. The wrong one of the two is always among the choices.
NEC 2026 314.28(A)(2)
13. A permanent barrier is installed in a pull box. How is each resulting section treated?
Show the answer
B. Each section is considered a separate box
A permanent barrier in a pull or junction box makes each section a separate box, so the pull distances get worked out section by section. A box that satisfies the multipliers overall can easily have one section that does not. That is the same idea the box fill rules use when they calculate each barriered space separately.
NEC 2026 314.28(D)
14. A junction box holding nothing but wire connectors is carried by the conduits entering it. Which support subsection governs?
Show the answer
A. The one for raceway supported enclosures without devices, luminaires or lampholders
The line in the support section is not spliced against unspliced. It is device against no device, and wire connectors and other splicing devices sit on the no device side of it. Putting a splice inside an enclosure does not move it into the stricter subsection, which is the single most common wrong belief on this topic.
NEC 2026 314.23(E)
15. An enclosure supported by entering raceways, holding no devices, has all of its conduit entries on the same side. How close to the enclosure is each conduit secured?
Show the answer
D. Within 18 inches
The general figure is 3 feet, and it tightens to 18 inches where every conduit entry is on the same side, because a one sided arrangement is a cantilever. The same subsection caps the enclosure at 100 cubic inches and asks for threaded entries or identified hubs with two or more conduits threaded wrenchtight. Grabbing the 3 feet without reading the same side condition is what this item is built on.
NEC 2026 314.23(E)
16. The exception that lets a single raceway support a conduit body no larger in trade size than the conduit names which wiring methods?
Show the answer
C. Intermediate metal conduit, rigid metal conduit, PVC, RTRC and electrical metallic tubing
The 2026 edition lists five methods here, and it also widened what the exception covers to include an FS or FD single gang device box and an explosionproof outlet box of any size with one or more entries. Read that list in your own book rather than from an older summary, because the shorter versions are the ones most published material still prints. The stricter subsection for enclosures with devices narrows the same idea to two methods.
NEC 2026 314.23(E)
17. What moves an enclosure from the looser raceway support subsection into the stricter one?
Show the answer
D. Mounting a device other than a splicing device in it, or hanging a luminaire or lampholder off it
The trigger is what is mounted in or on the enclosure, not what is joined inside it. Add a device that is not a splicing device, or support a luminaire or lampholder, and the securing distance tightens and the single raceway exception narrows. Same enclosure, same raceway, different answer, decided by the contents rather than by the splice.
NEC 2026 314.23(E), 314.23(F)
18. Under the subsection for raceway supported enclosures with devices, luminaires or lampholders, a single conduit may support a box or conduit body. Which conduits qualify?
Show the answer
B. Rigid metal conduit or intermediate metal conduit
The exception on the stricter side allows a single rigid metal or intermediate metal conduit and no others, and it names what it may support: a conduit body no larger in trade size than the conduit, an FS or FD single gang device box, or a single gang explosionproof outlet box of any size. The looser subsection permits five methods, so exporting that list here is the mistake. Threaded metal is what carries a device and its weight on one raceway.
NEC 2026 314.23(F)
19. An enclosure is mounted to the structural or supporting elements of a suspended ceiling. What size limit applies?
Show the answer
A. Not more than 100 cubic inches
The suspended ceiling subsection caps the enclosure at 100 cubic inches and then gives two ways to fasten it: to framing members by bolts, screws, rivets or identified clips, or to ceiling support wires that are taut and fastened at each end. The 100 cubic inch figure is the same ceiling that appears in the raceway support subsections, which makes it worth remembering once. The other numbers are box volumes from the metal box table, put there to look familiar.
NEC 2026 314.23(D)
20. What does the accessibility rule for boxes and conduit bodies actually protect?
Show the answer
C. The ability to get to the wiring and devices inside without removing part of the structure or the finish
The test is about the contained wiring and devices, and it is written against the finished building rather than against the installer at rough-in. If getting to the conductors means taking out part of the structure or the finish, the enclosure is not accessible. Underground enclosures are handled separately, so read what sits under the general sentence before calling a buried installation a violation.
NEC 2026 314.29
21. An outlet box encloses no devices and no utilization equipment. What minimum internal depth applies?
Show the answer
D. 1/2 inch
A box with nothing in it but conductors gets a floor of half an inch. Once a device or utilization equipment goes in, the depth is driven by the rearward projection of the equipment and by the size of the conductors supplying it, and the section gives a figure for each conductor range. Extension boxes, plaster rings and raised covers count toward that internal depth.
NEC 2026 314.24(A)
22. A box encloses a device supplied by 6 AWG conductors. What minimum internal depth does the section set?
Show the answer
A. 2-1/16 inches
Conductors of 8, 6 or 4 AWG put the box in one band with a depth floor of 2-1/16 inches. The bands below it are 1-3/16 inches for 12 or 10 AWG and 15/16 inch for 14 AWG and smaller, which is why those two numbers are sitting in the choices. The 2-1/8 inches is a box depth from the metal box table rather than a requirement from this section.
NEC 2026 314.24(B)(3)
23. A ceiling outlet is used exclusively for lighting. What weight does the box have to be able to support?
Show the answer
C. 50 pounds
A ceiling outlet used only for lighting is required to support a luminaire weighing at least 50 pounds. Above that weight the luminaire is supported independently of the box unless the box is listed for the load and marked on the interior with the maximum weight. The 35 and 70 pound figures belong to the paddle fan rules, and the 6 pounds is the small luminaire case on a vertical surface.
NEC 2026 314.27(A)(2)
24. An outlet box is the sole support of a ceiling suspended paddle fan. Which set of conditions applies?
Show the answer
B. Listed, marked on the interior as suitable for the purpose, marked with the maximum weight if it supports more than 35 pounds, and supporting no more than 70 pounds
Three conditions travel together for a box or box system used as the sole support of a fan, and the two weight figures are 35 pounds for the marking trigger and 70 pounds for the hard ceiling. The 50 pound figure belongs to the luminaire rule, which is why it reads plausibly here. Read which object the scenario describes before reaching for a number.
NEC 2026 314.27(B)(1)
25. What does the code require of every box in a completed installation?
Show the answer
A. A cover, faceplate, lampholder or luminaire canopy
Each box gets a cover, faceplate, lampholder or luminaire canopy, with a narrow exception for an installation covered by the luminaire article. A conduit body is finished with a cover, a lampholder or a device. Metal covers and plates are permitted, and where they are used they get connected to the equipment grounding conductors.
NEC 2026 314.25
One question a day keeps the habit, the practice exam runs the clock, and the tools page has the calculators and games.