Disconnecting Means Practice Questions

Every disconnect rule in the book is asking the same question, whether the person about to work on this equipment can kill the power and then see that it stayed dead. These questions work the two halves of the in sight from test and the section that now carries it, the lockable provision that stands in for line of sight, the disconnect rules in the motor, air conditioning and service articles, and the ratings and operating conditions the motor article sets for the device itself.

How to use these

Pick an answer and the explanation opens with the section it comes from. These are original questions written for this site, not questions from the exam. Have your own code book open: the Texas exam is open book, and looking the section up is the skill being tested.

Read the disconnecting means study page first if the topic is new to you.

1. Where the code says one piece of equipment shall be in sight from another, what has to be true?

Show the answer

A. It is visible from the other, and not more than 50 feet away from it

The rule is a pair of conditions and both hold or neither does. An installation can pass one and fail the other, which is exactly what a stem describing a plan view with a wall in it is built to test. Being in the same room is neither condition, since a room can be long enough to break the distance and a partition can break the visibility inside one room.

NEC 2026 110.29

2. In the 2026 edition, which section states the in sight from rule?

Show the answer

B. 110.29

This one moved. It reads as a rule in Article 110 rather than as a definition, and the service disconnect location rule points at that section by number. Section 430.102 is where the requirement lands on a motor circuit but it does not define the term. A candidate hunting the definitions for it will lose a minute before finding it.

NEC 2026 110.29, 230.70(A)

3. A motor controller sits 20 feet from its disconnect, with a partition wall between them. Does the disconnect satisfy the in sight from rule?

Show the answer

C. No, because the visibility half of the test fails

Distance passes and visibility fails, so the pair fails. Visibility is assessed as the installation stands rather than as anybody intended, which means a door that is kept shut is shut and shelving parked in front of a disconnect is in front of it. Sketching the layout in the margin before reading the options makes the wall much easier to see than it is in a sentence.

NEC 2026 110.29

4. A disconnect can be seen clearly from the equipment down a long open bay, but the measured distance is 60 feet. Does it satisfy the in sight from rule?

Show the answer

D. No, because the distance half of the test fails

This is the mirror image of the wall case. Visibility passes and distance fails, and again the pair fails. Marking the disconnect and keeping the aisle clear are both good practice and neither one is a condition in the rule, which is why two of the wrong options sound like a compromise an inspector might accept.

NEC 2026 110.29

5. Where the code lets a lockable disconnect stand in for one you can see, what does it require of the locking hardware?

Show the answer

B. The provisions for locking remain in place whether or not a lock is installed

The substitution only works if the locking hardware is there on the day the next person arrives, which is usually years after the installer left. A hasp that travels in somebody's van is not a provision for locking, and a breaker that only accepts an accessory nobody left on site is not lockable in the sense the code means. The lock itself does not have to be installed.

NEC 2026 110.25

6. The rule that locking provisions stay in place without the lock carries one exception. What does it cover?

Show the answer

C. A cord and plug connection

A cord pulled out of a receptacle is its own proof that the circuit is open, so the locking provision does not have to remain in place without the lock in that case. The industrial and over 1000 volt conditions are real, but they appear as conditions on other permissions in the motor and air conditioning articles rather than on this one. Reading an exception under the rule it actually modifies is the habit being tested.

NEC 2026 110.25

7. What does Article 430 require for each motor controller?

Show the answer

A. An individual disconnecting means, located in sight from the controller

Each controller gets its own disconnect and it goes where somebody working at the controller can see it. That is a separate requirement from the one protecting somebody working at the motor, and the two can be satisfied by one device only when that device is in sight from both places. The branch circuit protective device is a different element in the circuit and does not stand in for this.

NEC 2026 430.102(A)

8. Several coordinated motor controllers drive different parts of one machine. What does an exception to the controller disconnect rule permit?

Show the answer

D. A single disconnecting means for the group, located in sight from those controllers

The exception recognizes that one machine is one thing to work on, so one disconnect in sight from the group of controllers does the job the rule was written for. The in sight requirement does not go away, it just applies to the group. An out of sight disconnect with a label is a different permission, and it belongs to the circuits over 1000 volts.

NEC 2026 430.102(A)

9. A separate disconnecting means is provided for a motor. Where does it have to be?

Show the answer

B. In sight from the motor location and the driven machinery location

Two locations, not one. Somebody may be working at the motor or at the machine the motor drives, and a conveyor or a pump can put those in different places. The wording is why a disconnect at the motor on a piece of equipment whose drive end is around a corner can still fail. The controller end is protected by a different subsection.

NEC 2026 430.102(B)

10. May the disconnect required for the motor controller also serve as the disconnect for the motor?

Show the answer

C. Yes, if it is in sight from the motor location and the driven machinery location

One device can satisfy both requirements when it happens to be in sight from all three places, the controller, the motor and the driven machinery. That is common on a small package unit and rare on a long conveyor. Distance alone is not the test, since the visibility half still has to hold at each location.

NEC 2026 430.102(B)

Halfway

Ten down. If you want these timed and scored by content area, the practice exam runs thirty questions free, and the full bank of 178 plus the calculation ladder is $79 once.

11. The motor disconnect is not required at all under one exception. What has to be true?

Show the answer

A. The controller disconnect is lockable, and locating a motor disconnect is impracticable or introduces added hazards, or the site is an industrial installation with written safety procedures

The exception buys the same protection a different way, so it starts by requiring the controller disconnect to be lockable open. Then one of two situations has to hold, either the location is impracticable or hazardous, or the installation is industrial with written procedures and qualified persons. Horsepower on its own does not open the exception, though very large motors appear in the informational note as an example of added hazard.

NEC 2026 430.102(B), 110.25

12. What does Article 430 require of the way a motor circuit disconnecting means operates?

Show the answer

A. It opens all ungrounded supply conductors, no pole can be operated independently, and it cannot be closed automatically

All three conditions sit in one short section. The same section permits the disconnect to share an enclosure with the controller, which is why a combination starter is one box with two functions inside it. A device that could reclose on its own would defeat everything the disconnect exists for, which is the reason that sentence is there.

NEC 2026 430.103

13. A rooftop unit uses a hermetic refrigerant motor-compressor. Which article answers the disconnect question for it?

Show the answer

C. Article 440, which modifies the motor rules rather than replacing them

The scope of that article covers electric motor-driven air conditioning and refrigerating equipment and the circuits and controllers for it, and it adds what is needed for a sealed compressor that has no horsepower rating for the motor tables to work from. It modifies Article 430 rather than displacing it, so a rooftop unit can pull in both. Article 404 governs switches as devices, not where a disconnect goes.

NEC 2026 440.1, 440.14

14. A motor circuit has more than one disconnecting means between the branch circuit and the motor. What does Article 430 require about access?

Show the answer

D. At least one of them has to be readily accessible

The section is one line and it asks for at least one. That is a lower bar than it looks, because every disconnect in the circuit between the feeder or branch circuit and the motor still has to meet the type and rating sections. Readily accessible means reachable without climbing over or removing obstacles, which is a separate idea from being in sight.

NEC 2026 430.107, 430.108

15. A motor has a table full-load current of 14 amperes. A general-use switch is used as the disconnecting means. What minimum ampere rating does Article 430 set for that switch?

Show the answer

D. 28 amperes

A general-use switch used this way needs an ampere rating of not less than twice the full-load current, so 14 doubled is 28. The first figure is 115 percent, which is the general rating rule for a disconnecting means, and the second is 125 percent, which is the conductor rule. Three plausible percentages of the same current is how this item is built.

NEC 2026 430.109(A)

16. A general-use ac snap switch is used as a motor disconnecting means. It is rated 20 amperes. What is the largest motor full-load current it may serve?

Show the answer

A. 16 amperes

The condition on this permission runs the other way from the general-use switch rule. The motor full-load current has to be not more than 80 percent of the switch rating, so a 20 ampere switch tops out at 16 amperes. The switch also has to be one suitable for alternating current only rather than the general-use ac and dc kind.

NEC 2026 430.109(A)

17. A motor has a table full-load current of 14 amperes. What is the minimum current rating for its disconnecting means under the general rule?

Show the answer

B. 16.1 amperes

The general rating rule is 115 percent of the full-load current, so 14 times 1.15 is 16.1. That current comes from the motor table rather than from the nameplate, since the table values are what the code uses for conductor ampacity, switch ratings and branch circuit protection. An exception releases a listed unfused motor-circuit switch with a horsepower rating at or above the motor from the 115 percent figure.

NEC 2026 430.110(A), 430.6(A)(1)

18. Three motors drive separate parts of one woodworking machine. What does Article 430 permit for their disconnecting means?

Show the answer

D. A single disconnecting means for the group, rated for the combined load

The general rule gives each motor an individual disconnecting means, and the exception lets one device serve a group under any one of three conditions, the first of which is several motors driving parts of a single machine or piece of apparatus. The single device is then rated for the combined load. Horsepower does not enter into which condition applies.

NEC 2026 430.112

19. Where does the disconnecting means for air conditioning or refrigerating equipment have to be?

Show the answer

A. Within sight from and readily accessible from the equipment, and it is permitted to be on or within the equipment

That section asks for two things at once, line of sight and ready access from the equipment, and it then permits the disconnect to be mounted on or inside the unit itself. It also requires the working space rules to be met at the disconnect, which is easy to overlook on a crowded roof curb. A device in a panelboard two rooms away is in sight of nobody working on the unit.

NEC 2026 440.14

20. A disconnect is mounted on an access panel of a rooftop unit, over the equipment nameplate. What is wrong with that?

Show the answer

D. Both are prohibited, since the section bars mounting on panels designed to allow access to the equipment and bars a location that obscures the nameplate

The second paragraph of that section carries two prohibitions in one sentence and both are aimed at the same practical problem, that a service technician needs the panel to come off and the nameplate to be readable while the disconnect stays where it is. Being within sight does not rescue either one. This is the kind of detail that gets tested because it is invisible in a summary.

NEC 2026 440.14

21. A disconnecting means is installed in a commercial building. What does Article 110 require it to be marked with?

Show the answer

C. Its purpose, together with the identification and location of the circuit source that supplies it

The marking rule has two halves and the second one applies in other than one- or two-family dwellings. Both halves fall away where the disconnect is located and arranged so that the purpose, or the source, is evident on its own. The marking also has to be durable enough for the environment it sits in, which rules out a felt pen on a rooftop.

NEC 2026 110.22(A)

22. What does Article 230 require of the poles of a service disconnect?

Show the answer

B. It simultaneously disconnects all ungrounded service conductors it controls from the premises wiring system

Simultaneous opening is the point of the section, since a service disconnect that could leave one leg energized would put a working electrician in exactly the position the disconnect exists to prevent. A separate section handles the grounded conductor, requiring other means in the service equipment where the disconnect does not open it, and permitting a terminal or bus with pressure connectors for that purpose.

NEC 2026 230.74, 230.75

23. May a pole of a motor circuit disconnecting means open a permanently grounded conductor?

Show the answer

B. Yes, provided that pole cannot be opened without simultaneously disconnecting all conductors of the circuit

The permission exists so a switch can carry a pole in the grounded conductor, and the condition is what keeps it safe, since a grounded conductor opened while the ungrounded ones stay closed leaves the load energized and the return path broken. That condition is a design feature of the device rather than something field wiring can supply. It sits alongside the rule that no pole of the disconnect may be operated independently.

NEC 2026 430.105, 430.103

24. Where do the service disconnects for a one-family dwelling go?

Show the answer

D. In a readily accessible outdoor location, either on the dwelling or within sight of it

The 2026 rule splits by occupancy. One- and two-family dwellings take a readily accessible outdoor location, on the building or within sight of it by the same in sight rule used everywhere else, with an exception where an emergency disconnect is installed instead. The inside near the entrance option belongs to other occupancies. Bathrooms are barred outright for service disconnecting means.

NEC 2026 230.70(A)

25. How many service disconnects is a service permitted to have?

Show the answer

C. One, unless the conditions permitting two to six are met

The 2026 rule starts at one disconnect per service and then opens a path to two through six under a listed set of arrangements, such as separate enclosures each holding a single disconnect or switchgear with each disconnect in its own compartment. Disconnects that only cut power monitoring equipment, a surge device or certain control circuits are not counted against the number. Grouping on its own does not buy an unlimited count.

NEC 2026 230.71

Next

One question a day keeps the habit, the practice exam runs the clock, and the tools page has the calculators and games.

Free, weekly

One exam question a week, worked all the way through

A Texas journeyman or master item, the arithmetic shown, and a line on each wrong answer naming the mistake that produces it. Unsubscribe in one click.