Written against the 2026 NEC and checked section by section, September 2026
Motor Overload Protection Practice Questions
A motor circuit fails two ways that have almost nothing in common, so the code puts two devices on it and adds a third that protects nothing at all. These 25 items separate the overload device sized from the nameplate, the short-circuit and ground-fault device sized from the table, and the disconnecting means, then work the three overload percentages, the permitted increase and its ceiling, the thermal protector bands, and the control circuit rules alongside them.
Pick an answer and the explanation opens with the section it comes from. These are original questions written for this site, not questions from the exam. Have your own code book open: the Texas exam is open book, and looking the section up is the skill being tested.
Read the motor overload protection study page first if the topic is new to you.
1. What does the overload part of the motor article set out to protect against?
Show the answer
A. Excessive heating of motors, motor-control apparatus and motor branch-circuit conductors from motor overloads and failure to start
An overload is the motor running and drawing more than it should, heating slowly, with nothing actually broken. That failure takes minutes, while a fault takes milliseconds, so a single device cannot cover both. The short-circuit part of the article says in its own opening that it does not protect against overload.
NEC 2026 430.31
2. Which current is used to size a separate motor overload device?
Show the answer
B. The motor nameplate full-load current rating
The overload device is watching this particular motor, so it reads what this particular motor is rated to draw. That is the one place in a general motor application where the nameplate governs. Conductors, switches and the short-circuit device all come off the table instead.
NEC 2026 430.32, 430.6(A)(2)
3. A continuous duty motor rated 20 horsepower carries a nameplate full-load current of 28 amperes and a marked service factor of 1.25. At what current is the separate overload device selected to trip?
Show the answer
C. 35 amperes
The rule reads 1.15 or greater, so a 1.25 service factor qualifies for the higher base percentage of 125, and 28 times 1.25 gives 35 amperes. The 32.2 answer is 115 percent, which applies to a motor with neither qualifying marking. The 39.2 answer is the permitted increase, which is only reached after the base selection fails to start the motor.
NEC 2026 430.32(A)(1)
4. The same motor is replaced with one whose nameplate reads 28 amperes, no service factor, and a marked temperature rise of 55 degrees C. At what current is the overload device selected now?
Show the answer
D. 32.2 amperes
Neither qualifying marking is present, so the base percentage is 115 and 28 times 1.15 gives 32.2 amperes. A temperature rise above 40 degrees does not qualify, which is what the stem is checking. The 36.4 figure is this motor's permitted increase and not its base selection.
NEC 2026 430.32(A)(1)
5. Which nameplate marking earns the higher base overload percentage alongside a service factor of 1.15 or greater?
Show the answer
A. A marked temperature rise of 40 degrees C or less
Both markings describe thermal headroom, which is why they earn the same treatment. A service factor above 1.0 means the manufacturer rates the motor to deliver more than nameplate horsepower under defined conditions, and a low temperature rise means the windings run further below what the insulation can take. A motor with neither marking gets the smaller multiplier.
NEC 2026 430.32(A)(1)
6. The 28 ampere motor with the 1.25 service factor will not start on the overload device selected at the base percentage. What is the highest trip current the code permits?
Show the answer
B. 39.2 amperes
The permitted increase for a motor with a marked service factor of 1.15 or greater stops at 140 percent of the nameplate current, so 28 times 1.4 gives 39.2 amperes. The 36.4 figure is the ceiling for a motor with neither qualifying marking. Reading the wrong ceiling row is the error, because both are on the same short list.
NEC 2026 430.32(C)
7. A motor with no service factor marking and a temperature rise above 40 degrees C has a nameplate current of 28 amperes, and the base overload selection will not carry the load. What is the highest trip current permitted?
Show the answer
C. 36.4 amperes
The ceiling for a motor with neither qualifying marking is 130 percent, so 28 times 1.3 gives 36.4 amperes. Each of the three base percentages has a matching ceiling that sits above it, and the pairs have to be kept together. Mixing a base row with a different ceiling row is how 39.2 gets picked here.
NEC 2026 430.32(C)
8. A question gives a nameplate current and a service factor and says nothing about starting. Which value does it want?
Show the answer
D. The base percentage value, because the increase is a permission that only opens when the base selection fails
You size at the base percentage first, and the higher figure is available only where the device selected there will not start the motor or carry the load. A stem that never says the motor failed to start has not opened that door. Answering with the ceiling anyway is a wrong answer that looks like knowledge.
NEC 2026 430.32(C)
9. A thermal protector integral with a motor protects a motor whose table full-load current is 8 amperes. What is the maximum trip current permitted?
Show the answer
A. 13.6 amperes
The thermal protector allowance is set out as three bands by full-load current, and a motor at 9 amperes or less gets 170 percent, so 8 times 1.7 gives 13.6 amperes. Note that this percentage is applied to the table full-load current rather than to the nameplate, which is unusual inside the overload part of the article. The 12.48 answer is the middle band and 11.2 is the band for motors above 20 amperes, and both are on the list because people read the wrong row.
NEC 2026 430.32(A)(2)
10. The same kind of thermal protector is used on a motor whose table full-load current is 15 amperes. What is the maximum trip current permitted?
Show the answer
B. 23.4 amperes
A full-load current from 9.1 through 20 amperes falls in the middle band at 156 percent, so 15 times 1.56 gives 23.4 amperes. Above 20 amperes the allowance drops to 140 percent, which produces the 21 ampere distractor. The bands step down as the motor gets larger, which is the opposite of what people expect.
NEC 2026 430.32(A)(2)
Ten down. If you want these timed and scored by content area, the practice exam runs thirty questions free, and the full bank of 178 plus the calculation ladder is $79 once.
11. The familiar overload percentages of 125 and 115 apply to which motors?
Show the answer
C. Motors used in a continuous duty application and rated more than 1 horsepower
Two conditions gate that subsection, the duty classification and the horsepower, and the subsections that follow pick up the motors it leaves out. Check the size and the duty before you reach for a percentage. A one horsepower motor and a hoist motor both land somewhere else.
NEC 2026 430.32
12. A motor of 1 horsepower or less is started automatically. How is it protected against overload?
Show the answer
D. By one of the means the code lists for that case, including a separate overload device following the same percentage rule, a thermal protector or electronically protected motor, a device integral with the motor, or impedance protection
Automatic starting is what triggers this subsection, because nobody is standing there to notice the motor is not turning. The listed means are real alternatives rather than a preference order, and the separate overload device option follows the same percentages the larger motors use. A motor of that size started by hand is handled by the next subsection instead.
NEC 2026 430.32(B)
13. A portable motor of 1 horsepower or less is not permanently installed and is within sight from its controller. What does the code permit?
Show the answer
A. The branch-circuit short-circuit and ground-fault device may furnish the overload protection, and a separate exception allows any such motor on a 120 volt branch circuit protected at not over 20 amperes
Being within sight means a person can see whether the motor is running, which is the condition the relief is built on. The device furnishing that protection is still bounded by what the short-circuit part of the article allows. A motor of the same size that is not within sight from its controller goes back to the automatically started subsection.
NEC 2026 430.32(D)
14. Where does the article say overload protection is not required?
Show the answer
B. Where a power loss would cause a hazard, such as in the case of fire pumps
The judgment is that a fire pump stopping is worse than a fire pump burning up, so the provisions do not require the device that would stop it. The same part of the article also states that it does not apply to motor circuits above the stated voltage limits. Neither of those releases has anything to do with horsepower.
NEC 2026 430.31
15. Which current sizes the branch-circuit short-circuit and ground-fault protective device on a general motor application?
Show the answer
C. The full-load current from the Article 430 tables
That device is protecting the circuit rather than the motor, and it has to survive the starting current every time. Rather than send you chasing a locked-rotor figure for each unit, the code sets a maximum by motor type and device type and applies it to the standardized table value. Protecting the motor means nameplate, protecting the wire means table.
NEC 2026 430.6(A)(1), 430.52
16. Why does a dual element time-delay fuse get a lower percentage than a non-time-delay fuse in the branch-circuit device table?
Show the answer
D. Because it is built to ride through the starting current, so it does not need as much headroom above full-load current
Each column exists because that device type tolerates inrush differently, and the multiplier is set to whatever it takes to keep the device closed during a normal start. A fuse with no intentional delay needs three times the full-load current to survive that, and a time-delay fuse needs far less. Finding the right row and then reading the wrong column is the standard way to lose one of these items.
NEC 2026 Table 430.52(C)(1)
17. What overcurrent function does the disconnecting means for a motor circuit perform?
Show the answer
A. None, since it exists so the circuit can be opened for work on the motor
That is why the disconnect sits in a different part of the article from the two protective devices, with its own rules for what type qualifies and what current rating it carries. Its rating starts at 115 percent of the full-load current rather than the 125 percent people carry over from the conductor rule. The controller is a fourth thing again, and one enclosure often holds all three, which is precisely why the exam asks about them separately.
NEC 2026 430.109, 430.110(A)
18. A 15 horsepower motor on a 460 volt three-phase system has a nameplate reading 22.5 amperes, and Table 430.250 gives it 21 amperes. What is the minimum current rating of the disconnecting means?
Show the answer
B. 24.15 amperes
A switch is one of the three items the table governs, so the calculation starts from 21 amperes and not from the nameplate. That gives 21 times 1.15, or 24.15 amperes. The 25.88 answer applies 115 percent to the nameplate and the 26.25 answer applies 125 percent to the table value, and both are the mistakes this stem was written to catch.
NEC 2026 430.110(A), Table 430.250
19. Overload protection is shunted out during the starting period of a motor that is not started automatically. What condition does the code attach?
Show the answer
C. Fuses or inverse time circuit breakers rated or set at not over 400 percent of the motor full-load current are in the circuit and operative during starting
Something has to be watching while the overload device is out of the circuit, so the code requires a device sized high enough to pass starting current and low enough to catch a real problem. It also requires that the shunting means cannot be left in the starting position. On an automatically started motor the shunting is not permitted at all except under a separate and much narrower set of conditions.
NEC 2026 430.35
20. Fuses are used for motor overload protection on a three-wire, three-phase supply with one conductor grounded. Where do they go?
Show the answer
D. In each ungrounded conductor and also in the grounded conductor
The general rule is a fuse in each ungrounded conductor, and this particular supply arrangement adds the grounded conductor to that list. It is a narrow case and the option list is built to make the general rule look sufficient. Read the supply system named in the stem before answering, because the answer changes with it.
NEC 2026 430.36
21. A three-phase motor is protected by overload relays. How many overload units does the table require?
Show the answer
A. Three, one in each phase
The table is indexed by the kind of motor and the supply system, and every three-phase row asks for one unit in each phase. Single-phase rows generally ask for one, and two-phase rows for two. Answering with two on a three-phase motor is a habit left over from older installations and the table settles it.
NEC 2026 430.37, Table 430.37
22. A standard part-winding start induction motor is protected by separate overload devices. What does the code require?
Show the answer
B. Each half of the motor winding individually protected, with a trip current one-half of what would otherwise be specified
Each winding half carries about half the motor current, so a device sized for the whole motor would never see a problem in one half. The same section also cuts the branch-circuit short-circuit and ground-fault rating in half for each winding connection, with an exception where one device will let the motor start. Time-delay fuses under that exception are limited to 150 percent of the motor full-load current.
NEC 2026 430.4
23. A motor control circuit is tapped from the load side of the branch-circuit device. How are its conductors protected?
Show the answer
C. From the control circuit table, which varies by conductor size and by whether the conductors leave the motor control equipment enclosure
The control circuit has its own section and its own table, with separate columns for separate protection, for conductors kept inside the enclosure and for conductors that extend beyond it. One exception releases the requirement to short-circuit and ground-fault protection only where opening the control circuit would create a hazard, such as on a fire pump. Whenever a stem says control circuit, start-stop station or pilot device, this is the section it is pointing at.
NEC 2026 430.72, Table 430.72(B)(2)
24. A control circuit transformer has a rated primary current of 1.4 amperes. What overcurrent device is permitted in the primary circuit?
Show the answer
D. One rated or set at not more than 500 percent of the rated primary current
A transformer supplying a motor control circuit is excused from the general transformer overcurrent table and follows the motor control circuit section instead, which is a connection worth noticing before you meet it in a question. That section carries its own breakpoint below 2 amperes with a much larger multiplier. The other three answers are the general transformer percentages, offered because they are the ones people know.
NEC 2026 430.72(C)
25. A motor is used for a service that is inherently intermittent duty. How may it be protected against overload?
Show the answer
A. By the branch-circuit short-circuit and ground-fault protective device, provided its rating or setting does not exceed what the branch-circuit device table allows
A motor that stops on its own before it can cook is a different thermal problem from one that runs all shift, so the code lets one device cover both jobs within a stated limit. The section also repeats that any motor application counts as continuous duty unless the driven apparatus cannot run continuously with load. That default is what keeps this relief from swallowing the general rule.
NEC 2026 430.33