Multiwire Branch Circuits Practice Questions

Two circuits sharing one neutral is efficient wiring and a specific hazard, and the exam tests both halves. These 25 items work the Article 100 definition and the phase relationship it forces, the simultaneous disconnect at the origin and what a handle tie does about it, the grouping and identification rules that actually live in Article 200, what an open neutral does to the loads, and how the shared neutral is counted when conductors are bundled.

How to use these

Pick an answer and the explanation opens with the section it comes from. These are original questions written for this site, not questions from the exam. Have your own code book open: the Texas exam is open book, and looking the section up is the skill being tested.

Read the multiwire branch circuits study page first if the topic is new to you.

1. How does Article 100 describe a multiwire branch circuit?

Show the answer

A. Two or more ungrounded conductors with a voltage between them, plus a grounded conductor with equal voltage between it and each of them, connected to the neutral of the system

Every clause of that sentence does work. The voltage between the ungrounded conductors is what forces them onto different phases or different legs, and the equal voltage to the grounded conductor is what makes that conductor a neutral instead of just another circuit wire. A definition item on this topic is asking you to notice both clauses rather than one.

NEC 2026 Article 100

2. Why do the ungrounded conductors of a multiwire branch circuit have to come from different phases or different legs?

Show the answer

B. So that the shared neutral carries the difference between the load currents rather than their sum

It is not a preference and it is not about tidy panels. On the same leg the return currents add, and the neutral is asked to carry roughly double what it was chosen for with nothing in the circuit that would notice. The definition builds the phase relationship in by requiring a voltage between the ungrounded conductors.

NEC 2026 Article 100

3. A single-phase, 120/240 volt multiwire branch circuit is wired correctly. One circuit draws 16 amperes and the other draws 9 amperes. What does the neutral carry?

Show the answer

C. 7 amperes

With the two ungrounded conductors 180 degrees apart, the neutral returns only the difference between the two load currents, which is 16 minus 9, or 7 amperes. That is the whole point of the arrangement, since three conductors do the work of four. The 25 ampere answer is what the same two loads would put on the neutral if they were landed on the same leg.

NEC 2026 Article 100

4. Both ungrounded conductors of that circuit are accidentally landed on the same busbar leg. What happens?

Show the answer

B. The neutral carries 25 amperes and nothing in the circuit trips

The return currents now add instead of subtracting, so a conductor chosen to return one circuit carries the sum of two. No overcurrent device sees anything unusual, because each ungrounded conductor is still within its own rating. That silence is what makes this a routine inspection finding and an easy item to write, so a stem that describes where the breakers sit is asking about it.

NEC 2026 Article 100

5. A three-wire circuit is taken from a 208Y/120 volt system, with two ungrounded conductors and the neutral. Each of the two line-to-neutral loads draws 14 amperes. What does the neutral carry?

Show the answer

A. About 14 amperes

Two equal currents 120 degrees apart do not cancel, and their sum comes out about the same size as either one. Balance empties the neutral only where the ungrounded conductors sit 180 degrees apart. In a raceway this circuit looks identical to a single-phase three-wire circuit, which is why the code counts its neutral as current-carrying and the other one as not.

NEC 2026 310.15(E)(1)

6. What does Article 210 require at the point where a multiwire branch circuit originates?

Show the answer

B. A means that will simultaneously disconnect all the ungrounded conductors

Open one ungrounded conductor and the other is still driving current through the shared neutral, so somebody who switched off the breaker they were told to switch off is holding a live conductor. The requirement attaches at the origin and it is written as disconnection rather than as tripping. That distinction is what most items on this section are built from.

NEC 2026 210.4

7. Does the simultaneous disconnect requirement depend on what the multiwire branch circuit supplies at the far end?

Show the answer

C. No, it attaches at the point of origin and what sits downstream has no bearing on it

The single utilization equipment condition is real, but it belongs to a different subsection, the one that limits a multiwire branch circuit to line-to-neutral loads. Borrowing that condition and bolting it onto the disconnect rule is the invented answer these items are built around. An item will quote one of the two subsections and offer the other as a choice.

NEC 2026 210.4

8. When are individual single-pole circuit breakers with identified handle ties permitted as the protection for the ungrounded conductors of a multiwire branch circuit?

Show the answer

D. Where the circuit serves only dc line-to-neutral loads or single-phase alternating current line-to-neutral loads

That permission sits in the overcurrent article rather than in the branch-circuit article, which is why people go looking for it in the wrong place. It is conditioned on the kind of load and on the system, not on the occupancy or the panel. The handle ties themselves have to be identified for the purpose.

NEC 2026 240.15(B)

9. What is the difference between simultaneous disconnection and common trip on a multiwire branch circuit?

Show the answer

A. Simultaneous disconnection means throwing the handle takes both poles out together, while common trip means a fault on one pole opens the other as well

The branch-circuit article asks for disconnection, and a handle tie across two single-pole breakers provides it under the conditions the overcurrent article states. A two-pole common trip breaker also provides it and is what most panels get, but common trip is more than the section asked for. Reading the requirement as tripping rather than as disconnection produces the wrong answer on the handle tie item.

NEC 2026 210.4, 240.15(B)

10. What loads may a multiwire branch circuit supply?

Show the answer

B. Only line-to-neutral loads, unless one of the two exceptions applies

The general rule is a flat restriction, and both ways out of it are written as exceptions rather than as conditions inside the rule. One covers a circuit supplying only one utilization equipment, and the other covers a circuit whose ungrounded conductors are all opened simultaneously by the overcurrent device. Read the exceptions in your own book, because the second one is easy to confuse with the disconnect requirement two subsections earlier.

NEC 2026 210.4

Halfway

Ten down. If you want these timed and scored by content area, the practice exam runs thirty questions free, and the full bank of 178 plus the calculation ladder is $79 once.

11. Which of these permits a multiwire branch circuit to supply line-to-line loads?

Show the answer

C. The circuit supplies only one utilization equipment, or all its ungrounded conductors are opened simultaneously by the overcurrent device

There are exactly two exceptions and they are alternatives rather than a pair of conditions to be met together. The second one asks for opening by the overcurrent device, which is a stronger statement than the handle tie permission elsewhere. An answer built out of the disconnect rule is offered on purpose, because the two subsections sit a few lines apart.

NEC 2026 210.4

12. How are the ungrounded and grounded conductors of a multiwire branch circuit grouped?

Show the answer

D. By wire markers, cable ties or similar means, in at least one location within the enclosure

Article 210 states the grouping requirement and then points at the grounded conductor article for how it is done, so the mechanics are written one article over. Grouping exists for the next person opening that panel, since the hazard behind every rule on this topic is somebody working on a circuit they believe is dead. Two multiwire circuits arriving in one raceway both get tied.

NEC 2026 210.4, 200.6(B)

13. Which condition releases the grouping and identification requirement?

Show the answer

A. The branch-circuit or feeder conductors enter from a cable or a raceway unique to that circuit, which makes the grouping obvious

The exception is narrower than most people remember it, and it turns on a cable or raceway that belongs to that circuit alone. A tidy panel is not the test and neither is the breaker arrangement. Two multiwire circuits sharing one raceway fail the condition and get tied.

NEC 2026 200.6(B)

14. The 2026 edition carries a second exception to that grouping and identification requirement. What does it cover?

Show the answer

B. Branch-circuit conductors that pass through a box or conduit body without a loop of the kind the box fill rules describe, and without a splice or a termination

A conductor that only passes through has no connection anybody could work on in that enclosure, so there is nothing for the grouping to warn about. The exception borrows the loop description from the box fill rules, which is where a pass-through conductor is defined for counting purposes. A conductor that is spliced or terminated in the box is outside the exception.

NEC 2026 200.6(B), 314.16(B)(1)

15. Where do the conductors of a multiwire branch circuit have to originate?

Show the answer

C. From the equipment containing the overcurrent protective device, except as an underground provision permits otherwise

The general rule keeps the whole circuit tied to one piece of equipment, which is what makes a single simultaneous disconnect at the origin meaningful. The subsection carries a pointer to an underground wiring provision that permits an exception. A multiwire circuit assembled out of two different panels defeats every other rule on this page.

NEC 2026 210.4

16. The neutral of a 120/240 volt multiwire branch circuit opens between the panel and the loads. One load measures 24 ohms and the other measures 96 ohms. What does the 96 ohm load see?

Show the answer

D. About 192 volts

With the neutral gone the two loads become one series pair across 240 volts, so the current is 240 divided by 120 ohms, or 2 amperes, and the 96 ohm load sits at 192 volts while the 24 ohm load gets 48. The small load takes nearly the whole supply and burns out while the large one does nothing. Nothing trips, because 2 amperes is nowhere near either breaker rating, which is why the code refuses to let neutral continuity depend on a device connection.

NEC 2026 300.15(B)

17. What does the code say about the continuity of the grounded conductor in a multiwire branch circuit?

Show the answer

A. It shall not depend on device connections such as lampholders and receptacles, where removing the device would interrupt it

Pulling one receptacle out of a two-gang box should not put 200 volts on a lamp at the other end of the circuit, and that is exactly what a neutral run through the device terminals would do. The fix is a pigtail so the neutral stays made up whatever happens to the device. This is an overvoltage failure rather than an overcurrent one, and no protective device on the circuit will catch it.

NEC 2026 300.15(B)

18. May one neutral conductor serve two separate branch circuits that are not part of the same multiwire branch circuit?

Show the answer

D. No, unless the code specifically permits it elsewhere

A neutral conductor is not to be used for more than one branch circuit, more than one multiwire branch circuit, or more than one set of ungrounded feeder conductors unless the code says otherwise. That is what makes a shared neutral a defined arrangement rather than a shortcut. The section that says it also points at a separate common neutral provision for feeders.

NEC 2026 200.6(A), 215.14

19. Three-wire circuits are taken from a four-wire wye system and run in one raceway. How does the shared neutral count for the adjustment factors?

Show the answer

C. It is counted as a current-carrying conductor

That neutral carries about full load current when the two phases are matched, so it adds heat to the raceway and goes into the count on the system alone. The load type does not enter this case, because the geometry already settled it. The nonlinear trigger belongs to a four-wire wye circuit and reaches a different arrangement.

NEC 2026 310.15(E)(1)

20. Two single-phase three-wire multiwire branch circuits from a 120/240 volt system share a raceway, with linear loads. How many current-carrying conductors are there?

Show the answer

D. Four

Each circuit has two ungrounded conductors, which is four, and each neutral carries only the unbalanced current from the other conductors of its own circuit, so neither neutral is counted. That leaves four current-carrying conductors, which is already past three and puts the raceway in the first adjustment band. Counting the neutrals as well gives six, and a raceway with six conductors sits in the same band, so this error can hide.

NEC 2026 310.15(E)(2), 310.15(C)(1)

21. The same raceway is checked for conduit fill. How do the two neutrals count there?

Show the answer

A. Every conductor in the raceway counts for fill, including both neutrals and any equipment grounding conductors

Fill is about physical space, so a conductor takes up room whatever it is doing electrically. The derating count and the fill count are two different numbers taken off the same drawing, and a well-built item hands you one raceway and asks for both. A candidate carrying only one number in their head answers half of it correctly.

NEC 2026 Chapter 9 Table 1

22. A branch circuit serves life safety lighting and power in a health care facility. What does Article 517 say about it?

Show the answer

B. It shall not be part of a multiwire branch circuit

A shared neutral means one fault or one loose connection can take out both circuits at once, which is not acceptable where the lights are part of the life safety system. The rule is a flat prohibition with no conditions attached. It is a one line section and a clean item to write.

NEC 2026 517.15

23. Article 700 carries a matching rule. Which circuits does it reach?

Show the answer

C. The branch circuit serving emergency lighting and power circuits

The emergency systems article and the health care article carry the same prohibition for the same reason, and each names its own class of circuit. Knowing that the pair exists is worth more than knowing either one alone, because an item can be aimed at either article. Neither rule turns on the occupancy of the room the circuit lands in.

NEC 2026 700.19

24. What changed in the 2026 edition about identifying ungrounded branch-circuit conductors?

Show the answer

D. The article now carries a requirement for premises supplied from one nominal voltage system, as well as the existing rule for premises supplied from more than one

The single system case is new and it sends you to the general conductor identification rules, while the more than one system case keeps its own requirement to identify by phase or line and by nominal voltage system. An item that puts two systems in one raceway can be aimed at either article, depending on whether the stem asks about the neutral or about the phase conductors. Deciding which conductor the question is about is the whole item.

NEC 2026 210.5(C)

25. More than one nominal voltage system shares an enclosure with a multiwire branch circuit. What does the grounded conductor article require?

Show the answer

A. Each grounded conductor shall be identified by nominal voltage system

One system's grounded conductor may keep the ordinary white or gray finish, and the others take a different outer covering or another permitted means that distinguishes them. This is a separate requirement from the grouping rule, even though both sit in the same article and both come up in a crowded panel. An item about two systems in one enclosure is asking which of the two you noticed.

NEC 2026 200.6, 200.7

Next

One question a day keeps the habit, the practice exam runs the clock, and the tools page has the calculators and games.

Free, weekly

One exam question a week, worked all the way through

A Texas journeyman or master item, the arithmetic shown, and a line on each wrong answer naming the mistake that produces it. Unsubscribe in one click.