Temporary Installations Practice Questions

Article 590 starts by saying that everything the code asks of permanent work still applies, and every paragraph after that is either a named departure or an addition. These 25 items work the three permitted uses and the one day count that belongs to only one of them, the wiring methods that actually get relaxed, the ground-fault paragraph that is the most tested part of the article, the written program that stands in for devices in one narrow case, and the removal sentence people walk past.

How to use these

Pick an answer and the explanation opens with the section it comes from. These are original questions written for this site, not questions from the exam. Have your own code book open: the Texas exam is open book, and looking the section up is the skill being tested.

Read the temporary installations study page first if the topic is new to you.

1. What is the starting position of Article 590 on temporary installations?

Show the answer

C. Everything the code requires of permanent wiring applies, except where the article specifically modifies it

That default sits near the front of the article and every paragraph after it is either a named departure from it or an addition to it. Read it backward and a whole family of items becomes unanswerable, because you go looking for permission the article never grants. The reflex that works is to assume the ordinary rule applies and then check whether the article names the specific thing the question describes.

NEC 2026 590.4

2. Which use is limited to a period not exceeding 90 days?

Show the answer

D. Holiday decorative lighting and similar purposes

The 90 days is the only figure in days the time constraints contain, and it belongs to the seasonal category alone. A day count in an Article 590 item is doing one job, which is checking whether you hang the 90 days where it belongs or on a job trailer where it does not. Every other permitted use runs for as long as the work or the condition lasts.

NEC 2026 590.5(B)

3. How long is temporary wiring for construction, remodeling, maintenance, repair or demolition permitted to stay in service?

Show the answer

B. For the period of the work, with no day count stated

No calendar attaches to the construction category anywhere in the article. What ends the permission is completion of the work rather than the passage of time, which is why the removal sentence matters more here than a date would. Hanging the 90 days on a construction site is wrong twice over, since construction has no day count and the 90 days belongs somewhere else.

NEC 2026 590.5

4. A job is finished and the temporary wiring is still in place. What does the article say?

Show the answer

A. It is removed immediately upon completion of the construction or of the purpose it was installed for

This is the cleanest example of the point the whole article is making, which is that temporary describes a condition with a beginning and an end rather than a quality of workmanship. On an exam the item describes an installation that was compliant while the job was running, tells you the job finished, and asks about its status. The answer is not about how it was built, it is about the permission having expired.

NEC 2026 590.5

5. Which of these carries no stated time period in the article?

Show the answer

D. Emergencies, and tests, experiments and developmental work

Emergencies share one subsection with tests, experiments and developmental work, and no period attaches to any of them, so load testing a standby generator and a flood that took out the service sit in the same paragraph. Decorative lighting is the seasonal category with the 90 days on it, whatever the display is called. An item that asks whether one of these has a clock on it is checking exactly this.

NEC 2026 590.5

6. What does the article say about receptacles on a construction site?

Show the answer

C. They are all of the grounding type, and they are not installed on any branch circuit that supplies temporary lighting

Keeping receptacles off the lighting circuits means one tool faulting does not put everybody in the dark, which is a safety rule wearing an inconvenience. The grounding-type requirement has no exception, and where the raceway or cable armor does not qualify as an equipment grounding conductor, a separate equipment grounding conductor runs with the circuit. Ground-fault protection is an addition here rather than a substitute for grounding.

NEC 2026 590.6(C)

7. What does the article require of lamps used for general illumination on a temporary installation?

Show the answer

A. They are protected from accidental contact or breakage by a guard

The guard is an addition to the ordinary rules rather than a relaxation of them, and where the guard is metal and secured to conductive enclosure parts it gets connected to the circuit equipment grounding conductor. One exception releases nonreplaceable LED lamps that are integral to a listed temporary lighting string. Treating ground-fault protection as the only addition in the article is what costs items like this one.

NEC 2026 590.6(E)

8. What does the article require of decorative lighting used for holiday lighting?

Show the answer

B. It is listed and labeled on the product

The listing requirement is a short section near the front of the article and it pairs with the 90 day limit in the time constraints, which is the other rule aimed at the same installations. The wet location and ground-fault answers are real requirements in other places and neither is what this section says. The 30 day figure does not appear in the article at all.

NEC 2026 590.2

9. What does the article permit for Type NM and Type NMC cable used as temporary feeders?

Show the answer

B. They may be used in any dwelling, building or structure without limitation by building construction type and without concealment within walls, floors or ceilings

The relief in this article runs to getting conductors from the panel to the work, and this is the clearest example of it, since both of the ordinary limits on these cable types come off. Type SE gets the same treatment and may also be run in a raceway in an underground installation. None of that touches overcurrent protection, which still comes out of Article 240.

NEC 2026 590.6(A)

10. Where do the branch circuits of a temporary installation have to originate?

Show the answer

A. In an approved power outlet, switchgear, switchboard or enclosed panelboard, motor control center, or fused switch enclosure

The list is closed and it is the first thing to check when a stem describes a spider box or a homemade panel. Conductors may be cable assemblies or multiconductor cord or cable of the hard usage or extra-hard usage types, and they still get overcurrent protection out of the ordinary sections. An exception permits single insulated conductors for the emergency and test category where they are accessible only to qualified persons.

NEC 2026 590.6(B)

Halfway

Ten down. If you want these timed and scored by content area, the practice exam runs thirty questions free, and the full bank of 178 plus the calculation ladder is $79 once.

11. What disconnecting means does a temporary circuit need?

Show the answer

D. A suitable switch or plug connector that disconnects all ungrounded conductors of each temporary circuit, with a means to open a multiwire branch circuit simultaneously

Each temporary circuit gets a way to disconnect its ungrounded conductors, and a multiwire branch circuit gets a way to open all of them at once at the power outlet or panelboard where it originated. Identified handle ties are permitted for that. Plug connectors count, which is the part people miss when a stem describes cord-connected distribution.

NEC 2026 590.6(D)

12. Under what condition may a splice on a construction site be made without a box, conduit body or other enclosure?

Show the answer

C. Where the circuit conductors being spliced are all from nonmetallic multiconductor cord or cable assemblies and equipment grounding continuity is maintained

The general rule still wants a box with a cover installed, and the construction site exception is written around the cable type and the grounding path rather than around the connector or the location. A parallel condition covers metal-sheathed cable assemblies terminated in listed fittings that mechanically secure the sheath. Both conditions are about keeping the fault current path intact when the enclosure comes off.

NEC 2026 590.6(F)

13. Cable assemblies and flexible cords are installed as temporary branch circuits and feeders. Where may they not be run?

Show the answer

A. On the floor or on the ground

The support paragraph asks for intervals that keep the run from physical damage, using staples, cable ties, straps or similar fittings, and then refuses the floor and the ground outright for branch circuits and feeders. Extension cords are excused from that paragraph, which is the distinction a stem will turn on. Runs through doorways and other pinch points are permitted with protection provided rather than forbidden.

NEC 2026 590.6(I)

14. May a tree be used to support an overhead span on a temporary installation?

Show the answer

B. Only for holiday lighting arranged with strain relief or other approved means so movement of the vegetation does not damage the conductors

Vegetation is off the list for branch circuits and feeders generally, and the single exception belongs to the seasonal category and comes with conditions on how the span is rigged. That is one of the few places the article grants something the permanent rules refuse outright. Span length and cord type do not buy it.

NEC 2026 590.6(I)

15. Which receptacle outlets on a construction site get ground-fault protection for personnel under the temporary wiring rules?

Show the answer

C. All 125 volt, single-phase, 15, 20 and 30 ampere receptacle outlets that are not part of the permanent wiring and are in use by personnel

The ratings are specific and 30 amperes is on the list, which surprises people who carry the figures over from the general chapters. Read the voltage and ampere ratings out of your own copy rather than a remembered list, because the two sections are written separately and have not always matched. The paragraph reaches receptacles in use by personnel, which is the condition rather than the rating.

NEC 2026 590.7(A)

16. A receptacle that is part of the building's permanent wiring is being used for construction power. Does the ground-fault requirement reach it?

Show the answer

D. Yes, the article gives receptacles installed or existing as permanent wiring their own paragraph with the same protection

This is the feature that catches people, because the protection is not limited to receptacles installed as part of the temporary wiring. What triggers it is the use rather than the installation, since the site is wet, the tools take a beating and the cords get run over. An exception permits a listed cord set or device incorporating listed ground-fault protection and identified for portable use.

NEC 2026 590.7(A)

17. Two inspectors reach different conclusions about the same temporary wiring method on two sites. What in the article allows that?

Show the answer

D. A temporary wiring method is acceptable only where approved on the basis of the conditions of use and any special requirements of that installation

Approval based on conditions of use is written into the article, which is why the same detail can land two ways on two sites. That is a real feature of the section rather than an inconsistency to be argued away. It sits immediately beside the sentence saying the rest of the code still applies, and the two are meant to be read together.

NEC 2026 590.4

18. A 12 kW portable generator on a job site has 125 volt and 125/250 volt single-phase receptacle outlets. What does the article require?

Show the answer

C. Listed ground-fault circuit-interrupter protection for personnel on the 15, 20 and 30 ampere receptacle outlets that are part of the generator

The paragraph reaches generators of 15 kW or smaller and names 125 volt and 125/250 volt single-phase outlets at 15, 20 and 30 amperes. An exception permits a listed cord set or device with ground-fault protection identified for portable use, but only where the generator was manufactured or remanufactured before 2015. Receptacles used in damp or wet locations carry the ordinary wiring device requirements in addition to this.

NEC 2026 590.7(A)

19. For receptacle outlets the ground-fault paragraphs do not reach, what alternative does the article name?

Show the answer

B. A written assured equipment grounding conductor program, continuously enforced at the site by designated persons

The distinction an item wants here is that this is a program somebody runs rather than a thing you screw into a box, so a candidate carrying a rule of thumb that Article 590 never relaxes protection will strike this answer out and lose the mark. Ground-fault protection is still the other option in the same paragraph. The program covers cord sets, receptacles that are not part of the permanent wiring, and cord- and plug-connected equipment.

NEC 2026 590.7(B)

20. Under the assured equipment grounding conductor program, when are the required tests performed?

Show the answer

A. Before first use on site, where there is evidence of damage, before equipment is returned to service after repairs, and at intervals not exceeding 3 months

Four triggers, and the recurring one is 3 months rather than a month or six. Every equipment grounding conductor is tested for continuity and every receptacle and attachment plug is tested for correct attachment of the grounding conductor. The results are recorded and made available to the authority having jurisdiction, and so is the program document itself.

NEC 2026 590.7(B)

21. Where may an assured equipment grounding conductor program stand in for ground-fault protection on receptacle outlets in use by personnel?

Show the answer

C. In industrial establishments only, where only qualified personnel are involved, and only for outlets supplying equipment that would create a greater hazard if power were interrupted or whose design is not compatible with that protection

The exception is narrow on three axes at once: the kind of establishment, who works there, and what the outlet supplies. Read all three before answering, because a stem will satisfy one or two of them and leave the third out. Outside that exception, the receptacle paragraphs stand and the written program is the alternative only for outlets those paragraphs do not reach.

NEC 2026 590.7(A)

22. Temporary wiring on a site operates at over 600 volts. What does the article add?

Show the answer

A. Suitable fencing, barriers or other effective means limiting access to authorized and qualified personnel

Guarding is one short section and it is the only place in the article where the voltage of the installation changes what is required. Access control is the whole of it, so the answer is physical rather than electrical. The other three options are real requirements elsewhere in the code and none of them is what this section says.

NEC 2026 590.8

23. A solidly grounded wye temporary service is over 150 volts to ground but not over 1000 volts phase to phase, with available fault current greater than 10,000 amperes. What does the article require of the service overcurrent devices?

Show the answer

D. They are current limiting

This section was written because temporary service equipment takes abuse and gets reused, and the current-limiting requirement is the article's answer to a high available fault current. The same section asks that previously used devices be examined to confirm they were properly installed and maintained and show no evidence of impending failure. Ground-fault protection of equipment on a service is a different rule in a different article with its own trigger.

NEC 2026 590.9

24. A flexible cord enters an enclosure that contains devices requiring termination on a temporary installation. How is it secured?

Show the answer

B. To the box with fittings listed for connecting flexible cords and cables to boxes designed for that purpose

The relief this article grants runs to wiring methods and to splices, not to the way a cord lands in a box that holds a device. The fitting has to be listed for that job and the box has to be designed for it, which rules out a tie or a generic connector chosen on diameter. This sits immediately beside the splice paragraph, so an item can put the two together and see which relaxation you reach for.

NEC 2026 590.6(H)

25. A candidate is looking for the ground-fault requirement in Article 590 using a section number memorized from an older book. What should they do instead?

Show the answer

D. Find the rule by its heading, since at least one paragraph in the article sits at a different section number in this edition

The general requirements and the ground-fault requirements did not stay at the numbers an older tab points at, so a hunt by number on a timed exam is time you do not get back. The article is short enough to read front to back in one sitting, which is the argument for doing that once rather than trusting a tab. Ground-fault protection for personnel is still inside Article 590 and is written separately from the general chapter rule, so ratings do not carry from one to the other.

NEC 2026 590.6, 590.7