Written against the 2026 NEC and checked section by section, September 2026
Termination Temperature Practice Questions
The temperature limitation does not change what a conductor carries. It changes which column of Table 310.16 you are allowed to read the final answer out of, and it splits on one ampere figure and one conductor marking. These 25 items work the two subdivisions of 110.14(C)(1), the separate connector rule, and the arithmetic that follows when correction and adjustment run against a termination limit that gets no factors at all.
Pick an answer and the explanation opens with the section it comes from. These are original questions written for this site, not questions from the exam. Have your own code book open: the Texas exam is open book, and looking the section up is the skill being tested.
Read the termination temperature study page first if the topic is new to you.
1. Article 100 defines ampacity as which of these?
Show the answer
A. The largest current in amperes a conductor carries continuously, in the conditions it is installed in, without going past its temperature rating
Two phrases in that definition carry the weight. Continuously rules out momentary current, and under the conditions of use is what pulls in ambient temperature and the number of conductors bundled together. Notice the device rating is nowhere in it, which is why an ampacity question and an overcurrent question are two different questions even when they land on the same conductor.
NEC 2026 Article 100
2. The temperature rating associated with a conductor ampacity has to be coordinated so that it does not exceed what?
Show the answer
B. The lowest temperature rating of any connected termination, conductor, or device
The rule names three kinds of part and takes the lowest of them, so a lug, a breaker and the wire itself are all candidates. The insulation rating is only the answer when it happens to be the smallest of the three, which on ordinary gear it almost never is. Reading it as an insulation rule is how a candidate ends up sizing off the 90 degree column on equipment that cannot take it.
NEC 2026 110.14(C)
3. For circuits rated 100 amperes or less, or equipment marked for 14 AWG through 1 AWG conductors, the termination provisions default to which column?
Show the answer
C. The 60 degree column
This is the lower of the two doors into the section and it opens on the 60 degree column. The word or matters: the ampere rating is one trigger and the conductor marking on the equipment is a separate one, so a stem that gives you the terminal marking has handed you a route into the rule whether or not the ampere figure agrees.
NEC 2026 110.14(C)(1)(a)
4. For circuits rated over 100 amperes, or equipment marked for conductors larger than 1 AWG, the default column is which of these?
Show the answer
D. The 75 degree column
The upper subdivision defaults to 75 degrees, and it too has the two independent triggers. A 60 ampere disconnect whose lugs are marked for conductors larger than 1 AWG lands here on the marking alone, even though its ampere rating would have pointed at the other subdivision. Sorting on the ampere figure by itself is the mistake this pair is built to catch.
NEC 2026 110.14(C)(1)(b)
5. A conductor rated higher than the termination it lands on is permitted to be used for what purpose?
Show the answer
A. Ampacity adjustment, correction, or both
The section says so in its own opening sentence, which is what makes 90 degree insulation worth buying. You start from a bigger number and let ambient and conductor count eat into it before the termination check happens. It buys nothing where there is no derating to do, because with no factors applied the termination column is what you land on anyway.
NEC 2026 110.14(C)
6. Separately installed pressure connectors are used with conductors at ampacities not exceeding what?
Show the answer
B. The ampacity at the listed and identified temperature rating of the connector
A connector bought and installed apart from the equipment carries its own listing, and the conductor is held to what that connector is listed for. This is the honest route to a 90 degree termination in the field, and it is a listing question rather than a wire question. The subdivision sits in its own paragraph precisely because it is not tied to the 100 ampere split above it.
NEC 2026 110.14(C)(2)
7. Unless the equipment is listed and marked otherwise, the conductor ampacities used to determine equipment termination provisions come from which table?
Show the answer
C. Table 310.16, as appropriately modified by 310.12
The section names one table and one modifier. Table 310.16 is the raceway and buried table, and 310.12 is the dwelling service and feeder allowance that lets certain conductors be read at a reduced figure. Reaching for the free air table because the conductors are in free air somewhere in the run does not change what the terminations are judged against.
NEC 2026 110.14(C)(1), 310.12
8. Connectors and terminals for conductors stranded more finely than Class B and Class C stranding have to be what?
Show the answer
D. Identified for the specific conductor class or classes
Fine stranded conductor is what welding cable, generator leads and many battery connections are made of, and an ordinary set screw lug is not built to hold it. The classes themselves are shown in Chapter 9 Table 10. This sits in the opening paragraphs of the section rather than under temperature, which is why a candidate who only reads the temperature subdivision has never met it.
NEC 2026 110.14
9. Four current carrying 6 AWG THHN copper conductors run in a raceway at 40 degrees C ambient to terminations rated 75 degrees. What ampacity may be used?
Show the answer
A. 54.6 amperes
Start at the conductor rating: 6 AWG copper is 75 amperes in the 90 degree column. Correct for a 36 to 40 degree ambient at 0.91 to get 68.3, then adjust for four current carrying conductors at 0.80 to get 54.6. The termination limit is the plain 65 amperes in the 75 degree column with no factors on it, and 54.6 is the smaller of the two, so it wins.
NEC 2026 Table 310.16, Table 310.15(B)(1)(1), Table 310.15(C)(1), 110.14(C)
10. On a circuit rated 100 amperes or less, what does the section permit for motors marked with design letter B, C, or D?
Show the answer
B. Conductors rated 75 degrees or higher, with the ampacity not exceeding the 75 degree value
This is the fourth item in the lower subdivision and most candidates have never read it. It lifts a motor circuit off the 60 degree column and up to 75 without needing the equipment to be listed and identified for anything. A stem that names a design letter is pointing straight at it, which is the only reason the letter is in the stem.
NEC 2026 110.14(C)(1)(a)
Ten down. If you want these timed and scored by content area, the practice exam runs thirty questions free, and the full bank of 178 plus the calculation ladder is $79 once.
11. A 90 ampere noncontinuous load is fed from a device rated 100 amperes whose terminals carry no marking permitting higher temperature conductors. What is the smallest THHN copper conductor?
Show the answer
C. 2 AWG
The circuit is 100 amperes or less, so the answer comes out of the 60 degree column no matter what the jacket says. There 3 AWG is 85 amperes, which will not carry 90, and 2 AWG is 95, which will. Sizing from the 90 degree column gives 4 AWG at 95 amperes and reads as a tidy answer, which is exactly why it is sitting in the options.
NEC 2026 110.14(C)(1)(a), Table 310.16
12. A 200 ampere noncontinuous load runs on three current carrying copper conductors at 30 degrees C to 75 degree terminations. What is the smallest conductor?
Show the answer
D. 3/0 AWG
Over 100 amperes puts you in the 75 degree column, where 3/0 copper is exactly 200 amperes and 2/0 is 175. No correction applies at 30 degrees and no adjustment applies to three conductors, so the table figure is the answer with nothing done to it. Going up to 4/0 is not wrong on the wire, it is just larger than the code asks for and costs a mark.
NEC 2026 110.14(C)(1)(b), Table 310.16
13. What has to be true before a conductor may be used at its own higher temperature column at the terminations?
Show the answer
A. The equipment is listed and identified for use with conductors of that rating
The permission attaches to the equipment and to its listing, not to the wire. A number stamped near a terminal is a marking and not a listing, and the general rule applies unless the equipment is listed and marked otherwise. Most ordinary breakers, panelboards and safety switches are 75 degree equipment at best, so a stem that describes plain gear has already answered this without saying so.
NEC 2026 110.14(C)(1)
14. Six current carrying 10 AWG XHHW-2 aluminum conductors share a raceway at 30 degrees C with 75 degree terminations. What is the largest overcurrent device permitted?
Show the answer
B. 25 amperes
Work it in order. The 90 degree aluminum figure of 35 amperes adjusts at 0.80 for four to six conductors and gives 28, and the 75 degree termination figure of 30 is larger, so 28 is the usable ampacity. Then the small conductor rule caps the device for 10 AWG aluminum at 25 amperes, applied after the correction and adjustment factors. The cap is the answer, not the 28.
NEC 2026 240.4(D), Table 310.15(C)(1), Table 310.16
15. Do the ambient correction and conductor count adjustment factors get applied to the termination column figure?
Show the answer
C. No, the termination figure is read with no factors applied to it
Correction and adjustment belong to the conductor at its own rating. The termination figure is a plain table lookup that stands as printed, and the usable ampacity is whichever of the two comes out smaller. Applying the factors twice produces a number below what the code asks for, which oversizes the conductor and reads as the safe answer. It is still wrong.
NEC 2026 310.15(A), 110.14(C)
16. Three 4/0 aluminum XHHW-2 conductors feed a 250 ampere panel at 30 degrees C ambient on 75 degree lugs. What ampacity may be used?
Show the answer
D. 180 amperes
The 90 degree aluminum figure for 4/0 is 205, but nothing derates it here, so there is no headroom to spend. The circuit is over 100 amperes, which puts the terminations in the 75 degree column at 180 amperes, and that is the smaller number. The XHHW-2 rating has done no work at all in this problem, which is the point of the item.
NEC 2026 Table 310.16, 110.14(C)(1)(b)
17. Nine current carrying 10 AWG THHN copper conductors run at 45 degrees C ambient. What is the corrected and adjusted ampacity?
Show the answer
A. 24.4 amperes
Take 40 amperes from the 90 degree column, multiply by 0.87 for a 41 to 45 degree ambient in the 90 degree correction column, and multiply again by 0.70 for seven to nine conductors. That is 24.4 amperes. Starting from the 75 degree column and using its correction factor gives about 20.1, and it is wrong twice over: wrong column and wrong correction factor for the insulation you actually installed.
NEC 2026 Table 310.16, Table 310.15(B)(1)(1), Table 310.15(C)(1)
18. A 60 ampere fused disconnect has lugs marked for conductors larger than 1 AWG. Which column governs its terminations?
Show the answer
B. The 75 degree column, because the marking is an independent trigger
Each subdivision names two ways in and they are joined by or, so either one is enough on its own. The ampere rating here points at the lower subdivision and the conductor marking points at the upper one, and the marking carries it. This is why the terminal marking in a stem is never scenery, and why reading only the ampere figure hands you the wrong column.
NEC 2026 110.14(C)(1)(b)
19. Three 8 AWG THHN copper conductors run at 50 degrees C ambient to terminations rated 60 degrees. What ampacity may be used?
Show the answer
C. 40 amperes
The conductor side gives 55 amperes at 90 degrees corrected by 0.82 for a 46 to 50 degree ambient, which is 45.1, with no adjustment for three conductors. The termination side is the plain 60 degree figure of 40 amperes. Take the smaller, which is 40. Multiplying the 40 by the correction factor to get 32.8 applies a factor where none belongs and is the trap the fourth option collects.
NEC 2026 110.14(C)(1)(a), Table 310.16, Table 310.15(B)(1)(1)
20. Which of these does the temperature limitation rule not do?
Show the answer
D. It reduces the ampacity of the conductor itself
A 90 degree conductor stays a 90 degree conductor. Its insulation is unchanged and so is the current it can carry, and the section limits only the figure you are allowed to carry forward when you size against the load and the device. Holding that distinction is what lets you use the big column for the factors and the small one for the check without confusing the two.
NEC 2026 110.14(C)
21. Connection by wire binding screws or studs and nuts with upturned lugs is permitted for conductors of what size?
Show the answer
A. 10 AWG or smaller
The terminals subdivision sets that size limit and it is easy to miss because most reading of this section stops at temperature. Above 10 AWG the connection is made with a pressure connector, a solder lug or a splice to flexible leads. A terminal that takes more than one wire, and any terminal used with aluminum, each have to be identified for that duty, which is a separate sentence worth carrying.
NEC 2026 110.14(A)
22. Where does the code say tightening torque values for terminal connections come from?
Show the answer
B. From the equipment markings or the manufacturer installation instructions
The section points at the equipment and at the instructions that came with it, and it requires an approved means to actually reach the stated value. That last clause is the enforceable half: knowing the number does not satisfy it if nothing on site can apply it. The informational notes name torque tools and shear bolt style fasteners as examples of an approved means.
NEC 2026 110.14(D)
23. A run works out to a usable ampacity of 54.6 amperes. What standard overcurrent device may protect it under the next higher rating permission?
Show the answer
C. 60 amperes
Standard ratings run 50, 60, 70 in that stretch, so 54.6 falls between two of them and the permission lets you take the next one up, which is 60. Three conditions ride with it: the conductors are not part of a branch circuit supplying more than one receptacle for cord and plug connected portable loads, the ampacity does not correspond to a standard rating, and the selected rating does not exceed 800 amperes.
NEC 2026 240.4(B), Table 240.6(A)
24. A 1 AWG THHN copper conductor lands on a device rated exactly 100 amperes with no marking permitting higher temperature conductors. What ampacity does the section allow?
Show the answer
D. 110 amperes
Exactly 100 amperes falls inside the words 100 amperes or less, so you are in the 60 degree column, where 1 AWG copper is 110 amperes. The device rating is not the answer to an ampacity question; it is only what the conductor has to be able to carry. Reading 130 out of the 75 degree column is what an installer does when the wire is marked THHN and the gear is not listed for it.
NEC 2026 110.14(C)(1)(a), Table 310.16
25. Two conductors of different materials are placed under one terminal that makes physical contact between them. What does the code require?
Show the answer
C. The device has to be identified for the purpose and conditions of use
Conductors are not intermixed in a terminal, splicing connector or soldering lug where dissimilar conductors touch unless the device is identified for it. Size and temperature rating do not cure it, and neither does a compound: any compound used has to itself be identified for the use and be a type that will not harm the conductors or the equipment. The identification lives on the device.
NEC 2026 110.14
One question a day keeps the habit, the practice exam runs the clock, and the tools page has the calculators and games.