Transformer Calculations Practice Questions
Volt-amperes in equal volt-amperes out, so the kVA is the same number on both sides and every current in the problem comes from dividing it by the voltage on the side you were asked about. These 25 items work that division with and without the square root of three, then the protection percentages in Table 450.5(B), which is 450.5 in the 2026 book and was 450.3 in the 2023 one. Several run the secondary conductor rules that live in Article 240 rather than Article 450.
Pick an answer and the explanation opens with the section it comes from. These are original questions written for this site, not questions from the exam. Have your own code book open: the Texas exam is open book, and looking the section up is the skill being tested.
Read the transformer calculations study page first if the topic is new to you.
1. A 15 kVA single-phase transformer has a 480 volt primary. What is the rated primary current?
Show the answer
A. 31.3 amperes
Single-phase current is the volt-amperes divided by the voltage, so 15,000 divided by 480 is 31.3 amperes. The 62.5 figure is the secondary current if the secondary is 240 volts, and it belongs to the other side of the problem. Writing primary and secondary on the page before dividing anything is what keeps the two apart.
NEC 2026 450.5
2. A 75 kVA three-phase transformer has a 480 volt primary. What is the rated primary current?
Show the answer
B. 90.2 amperes
Divide 75,000 by 480 and by the square root of three: 480 times 1.732 is 831, and 75,000 over 831 is 90.2 amperes. Leaving the square root out gives 156.3, which lands in a plausible range and is the single most productive error on this subject. The factor belongs in three-phase work and nowhere else.
NEC 2026 450.5
3. Which quantity is the same on both sides of a transformer for exam purposes?
Show the answer
C. The kilovolt-ampere rating
Power in equals power out apart from losses the paper ignores, so the kVA is one number written once. Voltage and current move in opposite directions in proportion, which is where every ratio in the topic comes from. Conductor size follows from the current on each side and comes out different on each side for that reason.
NEC 2026 450.5
4. The same 75 kVA transformer has a 208Y/120 volt three-phase secondary. What is the rated secondary current?
Show the answer
D. 208.2 amperes
Same kVA, different divisor: 208 times 1.732 is 360, and 75,000 over 360 is 208.2 amperes. The 360.6 option is what you get by dividing by the voltage alone and then treating the square root of three as a multiplier, which reverses the arithmetic. Divide by both the voltage and the factor, every time.
NEC 2026 450.5
5. In the 2026 edition, overcurrent protection for transformers is found at which section?
Show the answer
A. 450.5
Listing requirements went in at 450.2 and reconditioned equipment at 450.3 for this cycle, and the rest of Part I slid down by two to make room. A tab set for the older book opens on reconditioned equipment, whose two subsections are both reserved, and the minute spent working out why is a minute you did not have.
NEC 2026 450.5
6. Which table carries the protection percentages for a transformer rated 1000 volts or less?
Show the answer
B. Table 450.5(B)
The section splits by voltage band before anything else. The over 1000 volt table carries impedance columns and a supervised location row, and using it on a 480 volt unit produces percentages that do not belong to the problem. Check the band, then open one table and stay in it.
NEC 2026 450.5(B), Table 450.5(B)
7. Within the table for transformers 1000 volts or less, what decides which row you read?
Show the answer
C. Whether the installation has primary protection only or protection on both the primary and the secondary
Two rows, two different answers for the same transformer, and the question tells you which one applies before it asks for a number. Impedance decides rows in the table for units over 1000 volts and in the footnote about coordinated thermal overload protection, but it does not pick your row here. Read the protection arrangement out of the stem first.
NEC 2026 Table 450.5(B)
8. Which of these is outside the scope of Article 450?
Show the answer
D. A current transformer
The scope excludes a list of eight kinds of transformer, and current transformers head it. Also out: dry-type units that are a component part of other apparatus, transformers integral to X-ray and similar apparatus, Class 2 and Class 3 transformers, sign and outline lighting, electric-discharge lighting, power-limited fire alarm, and research and testing units under safeguards. Everything else is in.
NEC 2026 450.1
9. With primary protection only and a primary current of 9 amperes or more, what is the maximum device rating as a percentage of rated current?
Show the answer
A. 125 percent
That is the ordinary case and the one most journeyman items use. It also carries the footnote that lets you take the next higher standard rating when 125 percent does not land on one. The 250 percent figure belongs to the primary side of an installation that also has secondary protection, and mixing the two rows is the error the table is designed to expose.
NEC 2026 Table 450.5(B)
10. With primary protection only and a primary current of less than 2 amperes, what percentage applies?
Show the answer
B. 300 percent
The primary only row has three current bands and the percentage rises as the current falls, because a device sized at 125 percent of a very small current is smaller than the transformer inrush. Nine amperes and two amperes are the breakpoints. A 500 volt-ampere control transformer on a 480 volt primary draws about 1 amperes, which lands in the bottom band.
NEC 2026 Table 450.5(B)
Ten down. If you want these timed and scored by content area, the practice exam runs thirty questions free, and the full bank of 178 plus the calculation ladder is $79 once.
11. A 30 kVA three-phase transformer has a 480 volt primary and primary protection only. What is the largest standard device permitted?
Show the answer
C. 50 amperes
Primary current is 30,000 over 480 times 1.732, which is 36.1 amperes, and 125 percent of that is 45.1. That is not a standard rating, so the footnote lets you go up to the next standard rating, which is 50. A candidate who rounds 45.1 down to 45 has read the footnote backwards; it permits a higher rating, not a lower one.
NEC 2026 Table 450.5(B), Table 240.6(A)
12. A 112.5 kVA three-phase transformer has a 480 volt primary and primary protection only. What is the largest standard device permitted?
Show the answer
D. 175 amperes
Primary current is 112,500 over 831, which is 135.3 amperes, and 125 percent of that is 169.2. Standard ratings run 150, 175, 200 through that stretch, so the next one above 169.2 is 175. Stopping at 150 protects the transformer but answers a question the table did not ask, which was for the maximum.
NEC 2026 Table 450.5(B), Table 240.6(A)
13. Where the installation has protection on both the primary and the secondary, what is the maximum primary device as a percentage of primary rated current?
Show the answer
A. 250 percent
Adding a device on the secondary lets the primary device be much larger, because the secondary device is now the one holding the load. That single figure covers all three primary current bands in this row, so unlike the primary only row you do not have to check whether the current is above or below 9 amperes.
NEC 2026 Table 450.5(B)
14. With protection on both sides and a secondary current of 9 amperes or more, what is the maximum secondary device as a percentage of secondary rated current?
Show the answer
B. 125 percent
The secondary side of this row reads like the primary only row: 125 percent above 9 amperes and 167 percent below it, with the next higher standard rating permitted on the 125 percent figure. Where the secondary protection is required as many as six breakers or six sets of fuses may share the job, grouped together in one place, with their ratings added up and measured against the single device figure.
NEC 2026 Table 450.5(B)
15. A 75 kVA three-phase transformer, 480 to 208Y/120 volts, has protection on both the primary and the secondary. What is the largest standard primary device?
Show the answer
C. 225 amperes
Primary current is 90.2 amperes and 250 percent of that is 225.5, so the largest standard rating that does not exceed it is 225. The next higher standard rating footnote rides on the 125 percent cells only, so there is no rounding up out of this cell. That difference between the two rows is worth more marks than the arithmetic is.
NEC 2026 Table 450.5(B), Table 240.6(A)
16. A transformer is installed as a motor control circuit transformer. Which rule governs its protection?
Show the answer
D. The motor control circuit provisions in Article 430
The transformer section hands this case straight to the motor control circuit rules and takes it out of the table entirely. So a stem that says control circuit has told you which article you are in, and working the percentages anyway produces a defensible number that answers the wrong question. Read the description of the transformer before you read its rating.
NEC 2026 450.5(B), 430.72(C)
17. A 45 kVA three-phase transformer has a 208 volt secondary and protection on both sides. What is the largest standard secondary device?
Show the answer
A. 175 amperes
Secondary current is 45,000 divided by 208 times 1.732, which is 360, giving 124.9 amperes. At 125 percent that is 156.1, which is not a standard rating, so the footnote takes you up to 175. Answering 150 uses the next rating below and reads as the cautious choice, but the item asked for the maximum the table allows.
NEC 2026 Table 450.5(B), Table 240.6(A)
18. Which secondary arrangements may be considered protected by the primary overcurrent device?
Show the answer
B. A single-phase transformer with a two-wire secondary, or a delta-delta connected transformer with a three-wire secondary
Everything else is not considered protected by the primary device, which is the sentence a candidate who assumes the primary breaker covers the whole system has never read. Even for those two arrangements the permission is conditional: the primary protection has to comply with the transformer section, and the value may not exceed the secondary conductor ampacity times the secondary to primary voltage ratio.
NEC 2026 240.4
19. Under the 10 foot secondary allowance, a field installation has the secondary conductors leaving the enclosure where the supply connection is made. The transformer is 480 to 208Y/120 volts with a 100 ampere primary device. What floor does that condition put under the secondary conductor ampacity?
Show the answer
C. 23.1 amperes
Take one tenth of the primary device rating, which is 10, and multiply by the primary to secondary voltage ratio of 480 over 208, which is 2.31. That gives 23.1 amperes. Dividing by the ratio instead of multiplying gives 43.3 and is the same arithmetic upside down. This floor sits on top of the ordinary sizing to the load and to the device the conductors terminate in, so it does not replace them.
NEC 2026 240.21(C)
20. A 480 to 240 volt single-phase transformer has a 200 ampere primary device and 25 foot secondary conductors with no secondary overcurrent device. What minimum ampacity do those conductors need?
Show the answer
D. 133 amperes
The rule takes one third of the primary device rating and multiplies it by the primary to secondary voltage ratio. One third of 200 is 66.7, the ratio is 480 over 240, or 2, and the product is 133.3 amperes. Stopping at 66.7 is the whole calculation with the ratio left out, and it is the answer of somebody applying a feeder tap rule instead.
NEC 2026 240.21(C)
21. Which of these does the marking rule require on a transformer nameplate?
Show the answer
A. The impedance, for transformers 25 kVA and larger
The nameplate list runs to eight items: manufacturer, rated kilovolt-amperes, frequency, primary and secondary voltage, impedance at 25 kVA and larger, required clearances where the unit has ventilating openings, the amount and kind of insulating liquid where one is used, and for dry-type units the temperature class of the insulation system. Impedance is the one candidates forget, and it is the input the protection tables need for the coordinated overload footnote.
NEC 2026 450.13
22. What does Article 450 require for a transformer disconnecting means, other than a Class 2 or Class 3 unit?
Show the answer
B. It is within sight of the transformer, or in a remote location that is lockable open and field marked on the transformer
The section gives two ways to satisfy it and puts conditions on the second. A remote disconnect has to be lockable open and its location has to be marked on the transformer itself, so somebody arriving at the unit can find the way to kill it. An option that permits a remote disconnect with no marking has dropped the half of the rule that matters.
NEC 2026 450.16
23. An individual dry-type transformer of more than 112.5 kVA is installed indoors and does not qualify for either exception. Where does it go?
Show the answer
C. In a transformer room of fire-resistant construction with a minimum 1 hour fire rating
The 112.5 kVA figure is the line. At or below it the rule is a 12 inch separation from combustible material unless a fire-resistant heat-insulating barrier is used, and above it the unit goes in a rated room. The two exceptions turn on a Class 155 or higher insulation system, with either a barrier and stated clearances or a completely enclosed construction. A vault is what dry-type units rated over 35,000 volts get.
NEC 2026 450.21
24. Which dry-type transformer is permitted in a hollow space of a building not permanently closed in by structure?
Show the answer
D. A unit rated 1000 volts or less and not exceeding 50 kVA that meets the ventilation and separation rules
Three conditions ride together here: the voltage band, a 50 kVA ceiling, and compliance with the ventilation section and the 12 inch separation from combustible material. A unit that meets all of them is not required to be readily accessible, which is the point of the permission. Dropping the kVA limit turns a narrow allowance into a general one.
NEC 2026 450.15
25. As used in the transformer overcurrent section, what does the word transformer mean?
Show the answer
B. A transformer or a polyphase bank of two or more single-phase transformers operating as a unit
The section defines the word for its own purposes in its opening lines, and the bank case is what the definition is there for. Three single-phase units wired as a bank get protected as one transformer rather than three, so you work the percentages against the bank rating. Autotransformers have their own section and are not covered by this definition.
NEC 2026 450.5